You are again applying common sense (which I applaud), but it still amounts to making an interpretation. 544.1.2, which is obviously but a small part of Chaper 54, merely talks about MPB/MEB for an e-c-p which is a gas, water or other service which enters the premises; it says nothing about e-c-ps which aren't. Taking everything literally, that does not alter the fact that (without the application of common sense) 411.3.1.2 requires MPB/MEB for any e-c-p - it can still be compliant with Chapter 54 (particularly 544.1.1, relating to conductor sizing), even if it is not an e-c-p for which 544.1.2 is relevant.411.3.1.2 calls for main protective bonding conductors complying with Chapter 54.unless I'm missing something, nothing in 411.3.1.2 says that Main Protective Bonding is not required for e-c-ps which are not services entering the building; it appears to simply say that e-p-cs must have main protective bonding, without any (common sense) exclusions such as you are now suggesting.
....or am I missing the bit which says that?
Read 544.1.2
You will have noted that we are not disagreeing about what, on the basis of a common sense interpretation of the regs, is actually required. I would hope that you will sooner or later admit that such common sense interpretation often is required, in order to avoid silliness - although I don't think I would dare to 'hold my breath'!
Kind Regards, John.