Indeed - provided one is confident that a measurement not much over 23kΩ, if one ever got it (we agree, very unlikley), would still be over 23k if one measured it a few days, weeks or months later.23kΩ is the cut-off point, then.I'm happy enough with 10mA - which will be 'safe' for the vast majority of people (give or take consequential injuries due to 'jumps'/falls etc.).
Is not the whole reason for the measurements you advocate in order to identify a hitherto unexpected/unsuspected low impedance path to earth, whatever the reason for that path?You don't need to measure a metal waste in the ground - it should be main bonded.
Yes, but you appear to be saying, without qualification,that a metal bath which has a low resistance to MET (by implication, for any reason) 'needs to be bonded'- which will make people think of G/Y cables. Are you considering the path through copper pipe (to main bonding, hence MET) to represent that required 'bonding'?It is.However, and more to the point, I think that some may read your statement as implying that a measured resistance <23kΩ means that bonding is requiredBut, if extraneous, copper tube will be bonded so the value will be very low.- e.g. (per your measurement to MET) that bonding of the bath would be required if, for example, it were plumbed in copper (almost inevitably with a low resistance to MET).
See above. What you are saying makes total electrical sense. However, as I said, 'bonding' (of a bath) makes people think of G/Y cables (connected to bath), and I don't think you are really suggesting that such cabling is required just because a metal bath has a low impedance path to MET via copper pipework and main bonding (and/or incidental paths via CPCs etc.), are you?I'm still confused about what you are trying to say. Is it that a bath which is extraneous and bonded by the pipework will read as if it needs bonding? I.e. all bonded parts will give a reading which requires them to be bonded.
Kind Regards, John