Fair enough! (although, as I said, I think that, in practice, one might as well say 22Ω )22K between ExtCP and MET (to be measured). 1K assumed for body resistance.
Kind Regards, John
Fair enough! (although, as I said, I think that, in practice, one might as well say 22Ω )22K between ExtCP and MET (to be measured). 1K assumed for body resistance.
It may be a lot higher (long light circuit) than that of a pipe that may also be touched or possibly vice versa for a high current circuit and long pipe run.Can we perhaps start by agreeing that, in practice, the extraneous-c-p will have a (usually very) low impedance path to 'earth'/MET?
Yes, usually.If so, then the touch voltage (as a result of a fault) (between exposed-c-p and extraneous c-p) to which you refer will be essentially the same as the p.d. between exposed-c-p and earth/MET. Agreed?
Is what you are saying that -The requirements for 'normal ADS' are that disconnection times should be met (i.e. that fault current should be equal to at least the Ia of device) in the event of a direct short ('of negligible impedance') between L and the exposed CP. Particularly when Ze is very low, R2 could easily be more than 21.7% (50/230) of the total Zs, so that the p.d. between the exposed-c-p and the MET could easily be greater than 50V (until disconnection occurs) in an ADS-compliant circuit. Put another way, 'normal ADS' requires that disconnection times be met when the voltage between exposed-c-p and MET is above some value, but that value may well be >50V. For the purpose of the subsequent discussion, let's just guess that, in a particular situation/installation, this 'some value' is 75V.
Well, yes but isn't that the point?On that basis, if you accept the initial point I made (that the touch voltage will essentially be the same as the p.d. between exposed-c-p and earth/MET), this means that 'normal ADS' disconnection time requirements would not necessarily be satisfied (i.e. fault current would be less than Ia) when the 'touch voltage' was only 50V (it might require, say, 75V). However, the regs require that SB achieves a situation in which the disconnection time requirements are met with a touch voltage (hence roughly the exposed-cp to MET p.d.) of 50V. This is a more exacting requirement than for 'normal ADS', and one way of looking at the effect of 'effective SB' is that it has to reduce the impedance of the path from exposed-cp to MET to the extent that this 'more demanding than usual' disconnection time requirement will be met.
Well, yes but its purpose is to safeguard the person; the facilitating is a secondary effect achieved by the 'bonding'.Since, in the situation I have described, the required disconnection with a touch voltage of 50V would not occur the absence of the SB, one can look at the SB as (partially) facilitating the required disconnection (at 50V touch voltage), which is functionality we would usually call 'earthing'.
Again - well, yes but the ADS is satisfactory unless the location requires bonding - supplementary for additional protection.This is where the reciprocity comes in. If one installs SB to reduce the exposed-cp to MET impedance such that Ia will be achieved (hence satisfactory disconnection) when the 'exposed-cp to MET' PD is only 50V (which sounds like earthing), then it will follow that the touch voltage will also be limited to 50V during the period until disconnection occurs (which sounds like bonding)...
Yes, I see that but I do think you are playing with the words to a certain extent.... so I guess you can really 'pay your money and take your choice'. If you take steps to make ADS happen when exposed-cp/MET pd is only 50V (earthing) (although 'normal ADS' might only require this to happen with a pd of, say, 75V) you will automatically have also limited the touch voltage to 50V (bonding). If you take steps to limit touch voltage to 50V (bonding), you will also have caused disconnection to occur when the exposed-cp/MET pd is lower than 'usual' (75V or whatever) for ADS (earthing)
You seem to have answered a slightly different question (about the R2 of a lighting circuit, rather than the path to earth via extraneous-cp) from the one I asked, but it seems that you probably agree that the two impedances/resistances are likely to be 'of the same order' (low or very low).It may be a lot higher (long light circuit) than that of a pipe that may also be touched or possibly vice versa for a high current circuit and long pipe run.Can we perhaps start by agreeing that, in practice, the extraneous-c-p will have a (usually very) low impedance path to 'earth'/MET?
Well ... It's not really "another way". If the CSA of the circuit's CPC (hence circuit's Zs) is, as may be the case, such that the pd between exposed-cp and earth (hence 'touch voltage') would be >50V (even though satisfactory 'normal ADS' was satisfied) then, no matter how one achieves it and what one calls it, one has to decrease the impedance of path between that exposed-cp and the MET (i.e. increase the effective CSA of that connection). One could do that by literally increasing the cable's CSA (or by running an additional cable/CPC in parallel with it), all the way back to the MET, or by running a cable from the exposed-cp to 'something else', maybe closer to hand, that had a low impedance path to the MET. In many/most circumstances, the extraneous-c-p would serve that purpose. So it's really more a question of 'the same', rather than 'another', way of restricting the touch voltage to 50V.Is what you are saying that -
a(nother) way to achieve the desired 50V touch voltage would be to increase the csa of the circuit cpc?
Sure, as above, it would usually be much more convenient to connect the required 'additional CSA') from the exposed-cp to some conveniently close low impedance path to the MET than to literally increasing the CSA of the circuit - and, as above, the local extraneous-c-p would serve that purpose....However, that may be difficult compared with a short piece of bonding.
No, you're thinking of Bernard, not meYes, I see that but I do think you are playing with the words to a certain extent. ... I think the trouble is that you do not really agree with the term bonding - joining parts not actually part of a circuit - and consider all G/Y to be earthing in one form or another.... so I guess you can really 'pay your money and take your choice'. ....
If you mean the one in which you stated the generally-agreed guidance on what constitutes and extraneous-c-p, then I have to say that I'm not really sure what point you are/were making. Everything discussed in this thread (including recent discussion about extremely improbable ones with relatively high resistance path to MET) has related to extraneous-c-ps that fulfill that definition/guidance.I take it that the reason for the first of my later posts has now become self evident?
I don't think that anyone has ever disagreed with any of that, but it does perhaps help to underline the complication which exists when one is talking about SB. In the case of SB, of course, the implicit requirement is not exactly to 'equalise' potential but to limit the potential difference to a maximum of 50V.'The purpose of protective bonding is to equalise potential rather than to carry fault current, although sometimes bonding conductors will also carry fault current where they form part of a parallel earth return path to the source of supply'
You are being over pedantic and argumentative.as Thripster reminded us earlier (and you often mention), the resistance/impedance to MET/earth of an extraneous-cp of can, in theory, be as high as 22kΩ (although goodness knows how that could happen). However, if that ever did happen, then all would be different, and one would definitely be talking about the need for 'true bonding' ...
That's all very true but, despite what you suggest, I don't think I have been pedantic and/or argumentative about any of it, nor even 'challenged' any of it! In fact, as I've said, the figure really makes little difference in practice - one can use 22kΩ (or 48kΩ if one wishes but, as I've said, in practice one could probably use, say 20Ω, since the it is incredibly unlikely that figures between that and 22kΩ (or 48kΩ will ever be seen in practice.You are being over pedantic and argumentative. ... As you know, (for others) the figure is derived from the value of 10mA being deemed safe. ... Actually the voltage used should be nearer 240V and therefore 24kΩ and accounting for the resistance of the body therefore completely pointless. ... Some say the figure should be 5mA and therefore 48kΩ. ... That the resistance measured will (virtually) never be anything near this does not detract from the relevance.as Thripster reminded us earlier (and you often mention), the resistance/impedance to MET/earth of an extraneous-cp of can, in theory, be as high as 22kΩ (although goodness knows how that could happen). However, if that ever did happen, then all would be different, and one would definitely be talking about the need for 'true bonding' ...
That's a very interesting question - and I suspect that the answer is probably that there is no test that would work satisfactorily ('be safe') in all situations.What would you state as the determining factor for deciding if extraneous or not?
As I said previously, if that scenario is thought to be a possibility then the part should be earthed and whether it was extraneous (before) or not is irrelevant; it now will be....if the extraneous-c-p were introducing a high (probably 230/240V) potential then the higher the resistance between that extraneous-cp and the MET (or an exposed-c-p), the higher would be the 'touch voltage' (pd between extraneous-cp and exposed-cp or MET/CPC). If one wants to cater for that situation (which BS7671 implicitly recognises as a possibility), it would surely be totally inappropriate (one might say crazy) to employ a definition which said that the part didn't qualify as an extraneous-cp, and therefore didn't need bonding, if the resistance between it and MET (or exposed-cp) was above some figure (whether that figure be 20Ω, 22kΩ, 48kΩ or whatever), wouldn't it?
Nor is this totally hypothetical. If the part in question were, say, a pipe which was normally electrically 'floating' (hence extremely high resistance to exposed-cp or MET - so you would say that it was not an extraneous-cp, and therefore didn't need bonding), if that were to somehow acquire a high potential relative to earth, then the touch voltage (between it and exposed-cp or CPCs/MET) would be the full 'introduced voltage' (quite probably 230/240V). Hence, despite the well-meaning 22kΩ (or 48kΩ criterion (intended to limit current through a person to 10mA), a part could satisfy 'the criteria' for not being an extraneous-cp, yet leave (in the absence of bonding) a situation in which at least a couple of hundred mA could pass through a person if they simultaneously touched it and something (e.g. an exposed-cp) connected to MET/earth.
But, that's not fair, is it?So, I don't really know what criterion for something being an exposed-cp would be 'safe' in all situations - but I do know (for reasons explained above) that the criterion being discussed would not be!
It was you that asked me what criteria could be used to define what was, and was not, an extraneous-cp - otherwise I probably would not have raised the matter!As I said previously, if that scenario is thought to be a possibility then the part should be earthed and whether it was extraneous (before) or not is irrelevant; it now will be.But, that's not fair, is it? An electrical installation has to be a compromise as not all possible occurrences can be safeguarded against at the same time.So, I don't really know what criterion for something being an exposed-cp would be 'safe' in all situations - but I do know (for reasons explained above) that the criterion being discussed would not be!
Yes, but the 23kΩ (or 48kΩ above which bonding is not necessary is adequate, albeit the actual figures a nominal limit.It was you that asked me what criteria could be used to define what was, and was not, an extraneous-cp - otherwise I probably would not have raised the matter!
But doesn't that definition relate to parts which are extraneous?Your view seems to be that, since "not all possibilities can be safeguarded against at the same time", we should restrict our thinking about extraneous-cps to their ability to 'introduce earth potential'. I accept that, given the rarity of the alternative possibilities, that might not be an unreasonable 'compromise' - but if that's what were wanted, then BS7671 really ought to remove the "usually" (earth potential) from it's definition of of an extraneous-cp. So long as the word remains there, the test we have been discussing is inadequate in relation to the definition.
Indeed - in fact, far 'more than adequate' in relation to an extraneous-cp which 'liable to introduce earth potential'.Yes, but the 23kΩ (or 48kΩ above which bonding is not necessary is adequate, albeit the actual figures a nominal limit.
So what do you think that BS7671 had in mind when it defined an extraneous-cp as a conductive part which is "liable to introduce a potential, generally Earth potential"? 'Generally' surely means/implies 'not always' - so what potentials (and situations) other than Earth potential do you believe they were thinking of, if not the possibility of the part (somehow) acquiring a potential above earth potential? ... or are you suggesting that they were wrong to include the word "generally"?We do not have to cater for the part becoming live by contact with a conductor.
Eh? I'm talking about BS7671's definition of what IS (and not) extraneous. If the definition only applied to things which we had already decided were extraneous, there would surely be no point in having a definition which told us what was (and what was not) extraneous, would there ?!!But doesn't that definition relate to parts which are extraneous?
Just that. It is 'usually' earth potential but 'not only' or 'not exclusively'.So what do you think that BS7671 had in mind when it defined an extraneous-cp as a conductive part which is "liable to introduce a potential, generally Earth potential"?We do not have to cater for the part becoming live by contact with a conductor.
No. I do not see the difficulty.'Generally' surely means/implies 'not always' - so what potentials (and situations) other than Earth potential do you believe they were thinking of, if not the possibility of the part (somehow) acquiring a potential above earth potential? ... or are you suggesting that they were wrong to include the word "generally"?
Of course the definition only applies to parts which we had already decided were extraneous; how could the definition of an extraneous-c-p apply to a part which isn't an extraneous-c-p?Eh? I'm talking about BS7671's definition of what IS (and not) extraneous. If the definition only applied to things which we had already decided were extraneous, there would surely be no point in having a definition which told us what was (and what was not) extraneous, would there ?!!But doesn't that definition relate to parts which are extraneous?
Needless to say, I don't believe that I'm mistaken but, yes, I am saying that there can be such a part - and that it would fulfill the BS7671 definition of an extraneous-c-p (since it may 'introduce a potential').I think what you are, in my view, mistakenly, getting at is that there can be an isolated part which cannot introduce earth potential but may introduce (up to) 240V.
Only if, per BS7671 definition, it is a conductive part of 'equipment' (which, in turn, BS7671 defines as "Any item for such purposes as generation, conversion, transmission distribution or utilisation of electrical energy") - and I really can't see that a bit of pipe appearing through a bathroom wall can qualify as such, can it?That then makes it an exposed-c-p doesn't it?
Please give me an example as I'm obviously missing something?Needless to say, I don't believe that I'm mistaken but, yes, I am saying that there can be such a part - and that it would fulfill the BS7671 definition of an extraneous-c-p (since it may 'introduce a potential').I think what you are, in my view, mistakenly, getting at is that there can be an isolated part which cannot introduce earth potential but may introduce (up to) 240V.
Well, then in that case it won't become live.Only if, per BS7671 definition, it is a conductive part of 'equipment' (which, in turn, BS7671 defines as "Any item for such purposes as generation, conversion, transmission distribution or utilisation of electrical energy") - and I really can't see that a bit of pipe appearing through a bathroom wall can qualify as such, can it?That then makes it an exposed-c-p doesn't it?
You appear to be working with your own concepts/definitions of "extraneous-c-p" and "exposed-c-p" to refer to any conductive parts that may introduce 'earth potential' and 'potentials above earth potential' respectively. Whilst those definitions are essentially self-fulfilling in relation to the arguments you are presenting, in neither case do they seem to correspond precisely with the BS7671 definitions. Whether your definitions or the BS7671 ones are the more useful/appropriate is, I suppose, a matter for debate!
You really should be asking the regs - it is they which have a definition of an extraneous-cp which, by implication, includes parts which can introduce a potential other than earth potential. I am really just the 'messenger'.Please give me an example as I'm obviously missing something?...yes, I am saying that there can be such a part - and that it would fulfill the BS7671 definition of an extraneous-c-p (since it may 'introduce a potential').
It won't become live unless something happens which you would probably say we 'do not need to safeguard against'.Well, then in that case it won't become live.... Only if, per BS7671 definition, it is a conductive part of 'equipment' (which, in turn, BS7671 defines as "Any item for such purposes as generation, conversion, transmission distribution or utilisation of electrical energy") - and I really can't see that a bit of pipe appearing through a bathroom wall can qualify as such, can it?