Under BS7671:2018+A1:2020 (as is valid until 27 sept) there are situations when both need to be completed, its not simple as the form makes out of being 1x for above 30mA, and 5x for 30mA and below. .... RCDs for additional protection (which will be rated at 30mA and below) need to be tested at 5x
RCDs for fault protection need to be tested at 1x.
That's true.
I must say that I've never really understood the 5x requirement. I would say that one has to assume (because it's true) that, in terms of the current though a human being, 30 mA is enough to be potentially fatal, so it's the x1 test that primarily matters, and I very much doubt that any RCD which 'passed' the test at 1x would not also 'pass' at 5x. In fact, although my experience is limited, I'm not sure that I can personally recall an RCD which 'passed' tests at 1x which did not have a disconnection time
(at 1x) which would not have satisfied the (≤40 ms) requirement at 5x - and it seems inconceivable that any RCD would have a longer disconnection time at 5x than at 1x! Maybe I'm missing something, but that's why I've always felt that the x5 tests are probably pretty redundant/irrelevant.
In some instances, you might be using the same device to serve both purposes, such as a dual split board on TT (without separate 100S incommer) or a C type rcbo on a TN system where you cant meet the Zs for the overcurrent device (ergh) .... (Of course, for RCDs in excess of 30ma, they cant provide additional protection and testing at 5x has never been required)
All true.
But now they have changed it again, and we just test them all at 1x under BS7671:2018+A2:2022, I do wish they'd stop changing things!
Such changes are, indeed, annoying but, as you will realise from what I've written above, my personal view (for what it's worth) is tht they have now changed it to something more 'sensible'!
In any event, I would say that, in terms of protraction against electric shock, the distinction between 'additional' and 'fault' protection (provided by RCDs) is really fairly artificial. As you may aware, over the years I have repeatedly tried hard (here and many other places) to canvas reports of occasions of which people have experienced (and survived!) electric shocks which caused an RCD to trip, and have only ever managed to identify a couple of such reports.
That being the case, I would say that the main value of RCDs in providing protection against electric shock derive from what you would presumably call 'fault' protection - i.e. clearing a fault before anyone has received a shock. In that regard, they are far more 'sensitive' than OPD-mediated ADS, since they will operate in response to L-CPC faults of far more than 'negligible impedance' (but still capable of resulting in potentially lethal shocks) - whereas (particularly if Zs is close to 'the limit') OPD-mediated ADS will only give the required disconnection times if the fault is close to being of 'negligible impedance'.
As a final 'in passing' comment, I wonder whether it is ever necessary (in a domestic situation) to have a 300 mA up-front RCD, since I would have thought that 100 mA would always be adequate (and 'better'). In my TT installation, although all final circuits are protected by 30mA RCDs/RCBOs, I have up-front time-delayed RCDs to protect long distribution circuits - but they are 100 mA ones.
Kind Regards, John