Quite a standard facility with 16mm² insulated and sheathed cable in an average meter designed for 35mm²....Quite often with terminations like that, its possible to get a test probe down the side of the conductor and onto the live terminal,
Quite a standard facility with 16mm² insulated and sheathed cable in an average meter designed for 35mm²....Quite often with terminations like that, its possible to get a test probe down the side of the conductor and onto the live terminal,
As you imply, there are are a few electricians who have been authorised by a DNO to pull cutout fuses, but are even they allowed to 'interfere with' the meter tails, other than at the downstream end of the one coming from the meter?Unless the contrator is one of the rare breed still authorised to pull the cutout and carries registered crimpers
As you imply, there are are a few electricians who have been authorised by a DNO to pull cutout fuses, but are even they allowed to 'interfere with' the meter tails, other than at the downstream end of the one coming from the meter?
Yes probably. But DNOs operate to different regulations.When I had a main fuse upgrade (60A to 100A) the blokes from UK Power noted that the existing tails were non-compliant as they had the outer insulation (black) removed by a couple of inches to show the colours of the cables inside. This was done by the previous DNO in the 1980s when the cutout was leaking bitumen and they replaced everything. Anyway, the new cutout required new tails so all good.
Thanks.As you will realise, I was implying that such was what I suspected.I would say no.
That seems to be where people disagree, some seem to insist on a literal intepretation of the guidance and treat any basic insulation visible outside an enclosure as a C2, whereas others take a more nuanced view and conclude that a small ring of basic insulation visible for identification purposes is not a big deal.This issue would score C3 - improvement recommended - so the installation should be marked as satisfactory.
What 'guidance' would that be -is this NICEIC again?That seems to be where people disagree, some seem to insist on a literal intepretation of the guidance and treat any basic insulation visible outside an enclosure as a C2 ...
... which, as I have suggested, would seem to me to be a sensible view., whereas others take a more nuanced view and conclude that a small ring of basic insulation visible for identification purposes is not a big deal.
That's pretty 'extreme' - more so than anything I've personally seen before. It's usually just a few mm, as in the piccie I posted.This was what mine looked like two years ago before they were changed. I
I'd say approaching an inch was more typical.That's pretty 'extreme' - more so than anything I've personally seen before. It's usually just a few mm, as in the piccie I posted.
As I wrote, that's more in keeping with what I've seen...but much to my surprise a lot less shows, like 1-2mm at the meter, at the henley only 4 of the 8 show and they are quite modest.
Well "electrical safety first", but that's essentially the same thing.What 'guidance' would that be -is this NICEIC again?
Need I say more?Well "electrical safety first", but that's essentially the same thing.
It wouldn't (in my opinion!) be quite so 'bad' if they had included a "likely" in relation to touch, as well as in relation to contact with metalwork. I doubt that a significant number of people will ever go anywhere near meter/cutout tails, so is surely is exceeding UNlikely that they would ever touch the exposed insulation - even electricians usually only deal with tails when they have been de-energised!"Sheath of an insulated and sheathed non-armoured cable not taken inside the enclosure of an accessory, such as at a socket-outlet or lighting switch, where the unsheathed cores are accessible to touch and/or likely to come into contact with metalwork. (Note: Code C3 would apply if the unsheathed cores are not accessible to touch nor likely to come into contact with metalwork)"
I'd imagine that depends on where said meter and cutout are located.I doubt that a significant number of people will ever go anywhere near meter/cutout tails