I don't think it's as simple as you imply ...If a circuit is electrically compliant with a 30A BS3036 fuse then this could be replaced by a 40A MCB.
I think you're probably overlooking the fact that the 'design current' (essentially the 'maximum load'), Ib, of a circuit is effectively defined by the ';rating' (in) of the OPD, regardless of the nature of that OPD - in particular that if one increases the rating of the OPD from 30A to 40A then, regardless of the nature of the IOPDs, one will have increased the design current (hence maximum load) from 30A to 40A.
The CCC of a cable, Iz, is obviously the same for any given installation method, regardless of the nature or rating of the OPD. The 'worst case' (lowest CCC) allowed by the regs for a ring final circuit is 20A.
Given that 'lowest permissible CCC of 20A' ...
If the rating (In) of the OPD is 30A then the design current (maximum load) (Ib) is also 30A, regardless of the nature of the OPD. Since that Ib is appreciably less than double the Iz (of 20A), the designer may be satisfied that,even when the circuit is loaded to its full Ib, it is 'not likely' that any part of the cable of the ring circuit will be overloaded (as required by reg).
However, if the In of the OPD were increased from 30A to 40A (regardless of the nature of the OPDs), that would be exactly double the Iz (20A) and hence, if the circuit were loaded to its full Ib, it would be inevitable that part of the cable of the circuit would be overloaded unless the load were applied to the ring in a perfectly balanced fashion, so it could not be said that such an event was "not likely".