No ,you can't just swap the MCB for a higher rated one before establishing the size of the cable it's protecting.Does this mean I need to get a higher amp MCB for it?
I have only opened the consumer unit once to replace one of the other MCB's. Is it legal for me to replace or do i need to get a qualified electrician to do it?
Yes it is ,I just didn't see the lower info.Is it not the same as the printed one at the bottom then?
That's a very good question. I had the shower unit replaced some years ago. I THink it was a 9.5kw.No ,you can't just swap the MCB for a higher rated one before establishing the size of the cable it's protecting.
What exactly is the kilowatt rating of the shower ?
No, it was like for like.What did you replace in the past ? Hopefully not a higher amperage breaker than was there originally ?
Ok.No, it was like for like.
It was installed around 5 years ago by a electrician.Ok.
A 32amp circuit is wholly unsuitable for a 9.5kw shower. That would draw around 41 amps at 240 volts.
Hence the 32amp MCB is tripping. How many years has the shower been running on that breaker ?