Yes, Very good point.You should not change the MCB for one with a higher rating if that's your intention.
The person that installed the circuit has judged that a 32amp breaker was suitable to protect the circuit cable.
Your shower appears to be drawing current at a level that the existing cable is carrying at its upper limit within its method of installation.
Do yourself a favour and engage an electrician to install an upgraded circuit
I was in a house a few years ago where the house owner had his 9kw electric shower (with 6mm2 cable and protected with a 40A/30ma RCBO) changed to a hot&cold integrally pumped Triton AS2000XT shower and who ever had installed it had left the the same RCBO and wiring in place, don't know how the 6mm2 cable was terminated in the shower but the same cable certainly appeared to (rear) enter the shower, this shower probably only draws a amp or two so was/is this against regulations or, at least should the the RCBO have been changed to a 5A or whatever?.