Electrical Advise

Joined
7 Feb 2015
Messages
3
Reaction score
0
Location
London
Country
United Kingdom
If you have a 17th edition CU with RCD protection installed, and you want to spur of 2 sockets outside the bathroom ( which are on a 32 Amp protected main ring ) for a tower rail and underfloor wire heating would you still need to add the fused spurs ? or can i just spur for the radiator from one socket in to a wall plate direct and have the underfloor heating spur of another socket straight in the thermostat ?

I`ve did a bit of research and apparently this is debatable. Hope i can get some answers.

Thanks in advance.
 
Sponsored Links
The fused spurs are required, as the cables for the thermostat and radiator will not be suitable for use on a 32A circuit, and if no FCU, how do you expect to turn the radiator off when not required?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top