unable to contact wilo till monday and dont know how to open a ZIP file on there website.
basically these pumps were fitted recently
These were fitted xmas by another firm and the companies been told there wired wrong and I got the task of going to look and report back.
Now in the past, the old motors were direct via starters and start load has often tripped the mcb's often resulting in type D breakers in the panels.
I was also under the impression larger motors need overload protection, which was usually fitted on the contacters in the panel.
However these units are electronically controlled via data cables within the black box.
Therefore the 3 phase is now direct from the C16 Triple mcbs in 2.5 singles aprox 10 metres in galv 50 x 50 trunking , via 32a isolators, hence no contactors with no fitted overloads.
my question is would these motors still have a start surge or be ok on Type C breakers and would these new style motors have fitted protection negating need for fitted overloads in the panel.
The motors are rated at 14.5 amp yet when tested were only 2.4 amp, but assured that would increase on demand.
I just wanted a heads up before phoning Wilo and if to involved refer it back to someone more knowledgable
thanks
unable to contact wilo till monday and dont know how to open a ZIP file on there website.
basically these pumps were fitted recently
These were fitted xmas by another firm and the companies been told there wired wrong and I got the task of going to look and report back.
Now in the past, the old motors were direct via starters and start load has often tripped the mcb's often resulting in type D breakers in the panels.
I was also under the impression larger motors need overload protection, which was usually fitted on the contacters in the panel.
However these units are electronically controlled via data cables within the black box.
Therefore the 3 phase is now direct from the C16 Triple mcbs in 2.5 singles aprox 10 metres in galv 50 x 50 trunking , via 32a isolators, hence no contactors with no fitted overloads.
my question is would these motors still have a start surge or be ok on Type C breakers and would these new style motors have fitted protection negating need for fitted overloads in the panel.
The motors are rated at 14.5 amp yet when tested were only 2.4 amp, but assured that would increase on demand.
I just wanted a heads up before phoning Wilo and if to involved refer it back to someone more knowledgable