The inverters must have been fitted for a reason. What was the reason?
the old motors had independant inverters, the new motors come as a package with inverters mounted on them, these were fitted by another company
If you get them set up properly you dont need to change your mcb, and you certainly don't need a motor rated one.
It was yet another company setting them up, that said they want them changed and they are setting them up nationwide and also WILO technical dept have now said they need to be motor rated mcb's
Have the pumps actually been run, and the C16 breakers are tripping? If they are tripping, is that on powering up the inverter or on starting the motor, or after the motor has been running a while?
BTW, in your first post you said the old motors were started by contactors, and in this one you have said inverters?
Just out of curiosity, I had a look at the manual from WILO website for these pumps. Page 71 suggests either 25A fuses, or
Miniature circuit breaker tripping characteristic: B
• Overload: 1.13-1.45 x Inominal
• Short circuit: 3-5 x Inominal
No mention of type D breakers....