I have never done it on that model but there is no reason why you should not fit an external EXV.
Doing that will even give an extra hot "instant" storage capacity.
You dont need to fit anything else as long as you are aware that the boiler isolating valves could be closed and isolate the protective devices in the boler.
To guard against that it would be necessary to fit a PRV close to the new EXV.
You should not fit an isolating valve in series with the new EXV ( although it does make maintenance so much easier and I would often fit a tool operated valve but its not correct ).
Tony
Doing that will even give an extra hot "instant" storage capacity.
You dont need to fit anything else as long as you are aware that the boiler isolating valves could be closed and isolate the protective devices in the boler.
To guard against that it would be necessary to fit a PRV close to the new EXV.
You should not fit an isolating valve in series with the new EXV ( although it does make maintenance so much easier and I would often fit a tool operated valve but its not correct ).
Tony