This Potterton Suprima 120L is connected to a heat exchanger which in turn heats a swimming pool. The explosive ignition started after about 18 months and gradually got worse. The Corgi engineer contacted Potterton and they suggested getting the PCB upgrade kit, which consists of all the electronics and the electrodes. This seemed to solve the problem for about 2 weeks after which the problem returned. Potterton next suggested we change the gas valve, this made no difference. The new PCB has now been set up, which basically means the high and low fan speeds have been set. Still no difference. The burner has been checked for damage, there is none and it is as clean as it will ever be. The fan appears to work. You can unscrew half of it and watch it spin using the test switch on the back of the PCB.
This problem is not there all the time. If the boiler is in a continuous heat cycle, gas on for about 2 minutes, off for about 2 minutes, this will continue for several hours with perfect ignition every time. However it appears that if the boiler is off for some period of time, say 10 minutes, the next time it comes on, bang! and up to a 2 foot flame shoots from the flue. Of course it does not do it every time, which is why this problem is so elusive.
One thing that is noticeable is that when you listen to the ignition sequence, there is a variable gap between the end of the sparks and the gas lighting. Certainly, when there is a large gap (approx 1 second) you are virtually guaranteed a large bang. Small intervals can sometimes result in a bang.
One must not forget that this boiler did work for 18 months, but I am not yet convinced that this boiler ignition system is 100% reliable.
When the ignition sequence initially starts up, the fan turns on. At this point you can often smell unburnt gas coming out of the flue.
So the questions as I see it are:
1: When the gas valve shuts off, there must be gas left in the pipe between the valve and the fan. Is this gas somehow creeping up into the burner and not being cleared out completely from the flue the next time the boiler starts?
2: Is the flame detector shutting down the sparks before it should.
3: Because it seems to happen more after the boiler has been off a little while, is it an issue with temperature. Are there components on the PCB that are temperature sensitive?
4: Could it be a condensation issue? When the boiler turns off the fan stays on for another 5 seconds sucking in cold air to the burner.
I would like to know how this gas valve works. I read in another posting that it is a 2 stage operation. As far as I can see this is just a simple solenoid valve that turns on when the sparks start. I have measured the volts across the coil and it is correct (200Vdc).
Any clues much appreciated.
Graham
This problem is not there all the time. If the boiler is in a continuous heat cycle, gas on for about 2 minutes, off for about 2 minutes, this will continue for several hours with perfect ignition every time. However it appears that if the boiler is off for some period of time, say 10 minutes, the next time it comes on, bang! and up to a 2 foot flame shoots from the flue. Of course it does not do it every time, which is why this problem is so elusive.
One thing that is noticeable is that when you listen to the ignition sequence, there is a variable gap between the end of the sparks and the gas lighting. Certainly, when there is a large gap (approx 1 second) you are virtually guaranteed a large bang. Small intervals can sometimes result in a bang.
One must not forget that this boiler did work for 18 months, but I am not yet convinced that this boiler ignition system is 100% reliable.
When the ignition sequence initially starts up, the fan turns on. At this point you can often smell unburnt gas coming out of the flue.
So the questions as I see it are:
1: When the gas valve shuts off, there must be gas left in the pipe between the valve and the fan. Is this gas somehow creeping up into the burner and not being cleared out completely from the flue the next time the boiler starts?
2: Is the flame detector shutting down the sparks before it should.
3: Because it seems to happen more after the boiler has been off a little while, is it an issue with temperature. Are there components on the PCB that are temperature sensitive?
4: Could it be a condensation issue? When the boiler turns off the fan stays on for another 5 seconds sucking in cold air to the burner.
I would like to know how this gas valve works. I read in another posting that it is a 2 stage operation. As far as I can see this is just a simple solenoid valve that turns on when the sparks start. I have measured the volts across the coil and it is correct (200Vdc).
Any clues much appreciated.
Graham