I still don't see (in this context) the relevance of the distance - as far as I am aware, the main concern, in some's people's minds, relates to the very rare occurrence of the MET of a TN-C-S installation rising to a very high potential relative to true earth - and that would be as much a problem if the outbuilding was 2 metres from the MET as it would if it were 200 metres away.
Well yes, but I doubt it is like that because of what we are discussing.
I still don't see (in this context) the relevance of the distance - as far as I am aware, the main concern, in some's people's minds, relates to the very rare occurrence of the MET of a TN-C-S installation rising to a very high potential relative to true earth - and that would be as much a problem if the outbuilding was 2 metres from the MET as it would if it were 200 metres away.
It's not relevant but (some) people advocate TTing an outbuilding because they dislike "exporting" the TN earth but don't consider an outside tap which may be farther away.
It's not relevant but (some) people advocate TTing an outbuilding because they dislike "exporting" the TN earth but don't consider an outside tap which may be farther away.
Well, in that case we can probably agree that 'they' simply aren't being logical or consistent. However, for a person (not me) who is concerned about the extremely low risk that we're talking about, I suppose that their mistake is in not realising that it also applies to the tap, not in being concerned about "exporting" a TN-C-S earth to an outbuilding.
In fact, accepting that it is an incredibly small risk that they are worrying about in the first place, I would think that the tap probably poses a (relatively) greater potential hazard than do most outhouses to which a TN-C-S earth is "exported", particularly if the outhouse doesn't have any extraneous-c-ps.
The earthing conductor must be an insulated copper conductor.
For domestic the tails are generally 16mm^2. With 16mm^2 tails the earthing conductor must be a minimum of 10mm^2. Where buried if not mechanically protected by steel/heavy duty PVC conduit then it must be a minimum of 16mm^2.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local