External bypass valve with modern pump

Joined
7 Dec 2022
Messages
426
Reaction score
124
Country
United Kingdom
We are replacing our boiler (heat only) in the spring and I am just checking a few things.

I have read that the idea of the ABV is to allow a minimum flow through the boiler. When most of the TRVs start to shut, the pressure in the system increases and that opens the ABV.

But what happens if you are using constant pressure or proportional pressure mode? The pressure in the system would not increase, even when the TRVs have closed. So how does an ABV work in this situation?
 
Sponsored Links
What about when the CH motorised valve closes? You will need the ABV then unless you have a PDHW setup.
 
We are replacing our boiler (heat only) in the spring and I am just checking a few things.

I have read that the idea of the ABV is to allow a minimum flow through the boiler. When most of the TRVs start to shut, the pressure in the system increases and that opens the ABV.

But what happens if you are using constant pressure or proportional pressure mode? The pressure in the system would not increase, even when the TRVs have closed. So how does an ABV work in this situation?

In short, you shouldn't use CP or PP mode with a ABV, some pumps like the UPS3 don't even have true CC curves but most arn't too bad, did you have any particular boiler and pump in mind?
But you could install a NO (normally open) 2 port valve as a bypass, that will close once any zone (2 port) valve opens, it will only open when all zone valves are closed, you then only have to ensure that one rad is partially opened (with no TRV) to allow minimum flow when (if) all the TRVs are throttling down.
 

Attachments

  • Various Pumps Constant Curves.zip
    708.5 KB · Views: 3
Sponsored Links
I have to admit, one not a plumber, and two can't understand why one radiator is left without a TRV, I know my old house the largest radiator in the house output wise had no TRV, or lock shield valve, output control was with the fan speed. This worked A1 with the old non modulating boiler, but for them to work with a modulating boiler I would have thought pipe work needs to be in series not parallel?

Old school and collage it was in series, below each radiator there was a restriction, but mother's house all in parallel and the by-pass valve would open as the TRVs closed, and the return hot water would turn down the boiler output.

I see no reason why output pressure should not be used to control boiler output, but it all depends on how the boiler is designed, the idea of getting a load of parts, connecting them together, and crossing fingers it will work just seems wrong, engineer in this country means degree standard, so when we get a heating and ventilation engineer to design and set up the system they would, we hope actually design the system, if it was easy they would not need an University education so for the homeowner he just hopes his guy knows his job.
 
In short, you shouldn't use CP or PP mode with a ABV, some pumps like the UPS3 don't even have true CC curves but most arn't too bad, did you have any particular boiler and pump in mind?

It will probably be a Vaillant 418 Ecotec Plus with a Wilo pump.
 
Could you explain a bit more? I'm not following your train of thought :)
With an S plan system you will have the pump in a short (3min) overrun when both motorised valves have closed, the ABV then opens to allow water to flow hence saving the pump. With PDHW the CH motorised valve will be NO so no need for an ABV if you have a radiator always open.
 
With an S plan system you will have the pump in a short (3min) overrun when both motorised valves have closed, the ABV then opens to allow water to flow hence saving the pump

In this situation, if the pump is set to constant pressure mode, won't it throttle right back to maintain that constant pressure. In which case, there still won't be enough pressure to open the ABV. I have no idea whether this happens in practice! But it is the logical outcome.
 