I am saying that there is no way that the feed to the shed is going to pull 56 amps !
Why not?I am saying that there is no way that the feed to the shed is going to pull 56 amps !
20A radial is all you need.Why would the sockets in shed 1 not be run as a radial rather than a ring?
Why not?I am saying that there is no way that the feed to the shed is going to pull 56 amps !
Summerhouse on maximum demand and shed on maximum demand!
It's not a good set up!
Are you seriously suggesting that one should estimate 'maximum demand' by adding up the ratings of all the OPDs, without considering actual 'likely loading' and diversity? If you did that, what proportion of installations do you think would have a 'maximum demand' which was less that the rating of the cutout fuse, or of the main main switch (and perhaps also the CCC of the meter tails)?Why not? Summerhouse on maximum demand and shed on maximum demand! It's not a good set up!
Quite - and what are the chances that you would be using the running machine, heater and circular saw all simultaneously for any appreciable period of time? (I would imagine very low - in particular, a circular saw is generally a very short-term load). Also, do the pond pump and filter really take 3A each, or is that just the fuse rating of their supplies? I really think that the maximum likely load on all this is going to be pretty modest.The worst case maximum I will draw would be; Shed 2 - Running machine which has a 2hp motor approx. 1500W = 6.5A 2kW heater = 8.7A Lights – 2 at 60W = 1A
Shed 1 - Circular Saw = 1800W = 7.8A Pond Pump – 3A blagdon powersafe box Pond Filter –3A on blagdon powersafe box Lights – 4no at 60W = 1.1A
Total 31.1A
Quite, and if anyone was tempted to use the heater and running machine simultaneously, they wouldn't be running fast enough!Thanks John. I would say to use all at once wouldn't happen. I mean if the good wife was on the running machine and me using the circular saw outside (I'm a fair weather worker!) then the weather would be as such we wouldn't have the heater on so reducing the load more.
As I suspected - so there's another 5A or so you can take off the total. In terms of what you've said, I suspect that a realistic maximum design current (maximum current likely to be drawn for appreciable periods of time) is probably not going to be even 20A, certainly not a lot more.The pump and filter, I used the fuse rating. In reality they are both around 70watts.