Indeed. As I said/implied at the very start, that is my intention. I'll probably do it later today.As others have said, time to replace it if suspect, NHX are the current range and are readily available and at a low price
I might, just as a matter of interest, but it would make no sense not to 'throw it into the bin' afterwards. As you say, they cost virtually nothing, and if I'm replacing it because of 'uncertainties' about it, it would make no sense to use it again, regardless of what testing might show. In fact, given that it's 'only' a B6, I could theoretically test it 'in situ', since there is a small (8.5kW) shower (virtually never used) supplied by a B40 in that CU - and that ought to draw just about enough current to relatively safely test the B6's magnetic trip. I wouldn't personally attempt to 'test', by any method, the magnetic trip of an MCB requiring a higher trip current than a B6!That said, I'd be tempted to try and find a way to test the old one with a high current low voltage AC source before slinging it into the dustbin.
There is seemingly nothing wrong with the circuit. Once the fuse was replaced, it works fine, with a plenty low enough Zs and it IRs OK.I've actually seen a fault (caused by a crushed cable) on a 1.5mm blow itself clear before a breaker tripped, but that was on a federal stablok type 4 Zs was out of spec at end of circuit, however probbaly wasn't at the point the fault occurred. Backup protection was BS88 100A which also stayed intact.