Hello Everyone,
further working down the list of my recent EICR findings...(last item actually)
This item reads: No end to End continuity of the Rn conductor CCT No:3 (Marked as FI)
CCT 3 is obviously a ring main, serving 3 rooms and two UFHs with FCU. The values from the EICR are
r1 = 0.43
rn = >999
r2 = 0.71
r1+r2 = 0.78
So apart from the rn all looks pretty normal. I have had a lot of work done in relation to this circuit, but I have a suspicion where this issue might come from. My question is, how do I go about
a) confirming the fault
b) getting as close as possible to the problem (I might need to remove a skirting board, so I want to be sure before I do this)
So far I've opened just one socket and checked continuity with my cheap multi meter. Measured at the socket, I have continuity from L2L, N2N but actually no continuity from CPC2CPC...Furthermore, I do have continuity between cpc and neutral, which I am guessing is due to the setup that neutral is grounded somewhere at the power supply. If I short neutral with one of the cpcs, I do have continuity from CPC2CPC, but if I short the other neutral with one of the cpcs there is no continuity.
What I don't understand is that there seems to be continuity on rn, but the EICR suggests otherwise? Is this because the sparky would have tested at the CU and fully isolated the ring there to ensure resistance would not bypass by going via CPC?
And also, if they have found a value for r2, why do I not get continuity at the socket when measuring from CPC2CPC?
further working down the list of my recent EICR findings...(last item actually)
This item reads: No end to End continuity of the Rn conductor CCT No:3 (Marked as FI)
CCT 3 is obviously a ring main, serving 3 rooms and two UFHs with FCU. The values from the EICR are
r1 = 0.43
rn = >999
r2 = 0.71
r1+r2 = 0.78
So apart from the rn all looks pretty normal. I have had a lot of work done in relation to this circuit, but I have a suspicion where this issue might come from. My question is, how do I go about
a) confirming the fault
b) getting as close as possible to the problem (I might need to remove a skirting board, so I want to be sure before I do this)
So far I've opened just one socket and checked continuity with my cheap multi meter. Measured at the socket, I have continuity from L2L, N2N but actually no continuity from CPC2CPC...Furthermore, I do have continuity between cpc and neutral, which I am guessing is due to the setup that neutral is grounded somewhere at the power supply. If I short neutral with one of the cpcs, I do have continuity from CPC2CPC, but if I short the other neutral with one of the cpcs there is no continuity.
What I don't understand is that there seems to be continuity on rn, but the EICR suggests otherwise? Is this because the sparky would have tested at the CU and fully isolated the ring there to ensure resistance would not bypass by going via CPC?
And also, if they have found a value for r2, why do I not get continuity at the socket when measuring from CPC2CPC?