Ahhhhhhhhhhhhhhhhhhhhhhhhhh now he says!
Sorry i forgot why does this now change things?
Ahhhhhhhhhhhhhhhhhhhhhhhhhh now he says!
Ahhhhhhhhhhhhhhhhhhhhhhhhhh now he says!
Bit confused by your description.when i did the insulation resistance test at the fuseboard and got a dead short i then went to the first light split up the cables and tested everyone of them and all the readings came out fine.
Bit confused by your description.when i did the insulation resistance test at the fuseboard and got a dead short i then went to the first light split up the cables and tested everyone of them and all the readings came out fine.
When you say split the cables - do you mean you split loop in/loop out then insulation resistance tested L/N/E on these cables separately?
If so, do you now get perfect readings on the L/N/E between the CU and the first light fitting?
If those readings are correct when the switches are all on, the only options left are a faulty lamp, or one of the lampholders is faulty in such a way that the fault only shows when a lamp is inserted.
It does indeed sound a little strange. But if the IR tests on the cables are all fine then not sure what else to suggest!If those readings are correct when the switches are all on, the only options left are a faulty lamp, or one of the lampholders is faulty in such a way that the fault only shows when a lamp is inserted.
So when i go back to the fault tomorrow then this should be what i check next?
It does indeed sound a little strange. But if the IR tests on the cables are all fine then not sure what else to suggest!If those readings are correct when the switches are all on, the only options left are a faulty lamp, or one of the lampholders is faulty in such a way that the fault only shows when a lamp is inserted.
So when i go back to the fault tomorrow then this should be what i check next?
Despite this, i'm sure someone posted a problem with a lighting ciruit on here a while ago where a nail through a switch wire was causing periodic tripping under load but IR tests were fine. It was understandably a nightmare to locate.
Has the customer put any nails in the walls/shelves up etc?
Might be worth checking with the customer all the same - if not just to rule this problem out.Don't think he's put any shelves up but he has had a builder in insulating the walls and so they might have caught it then, i hope its not as it'll mean re-wiring the circuit.
No idea. Are they standard ceiling pendants or more elaborate fittings of the finest Chinese manufacturing quality?What is the mlikely hood of it being a faulty lamp or lamp holder?
The problem is you say you have perfect IR readings with nothing connected in circuit. If you rewire the lighting circuit and put the old fittings back up you may have the same problem and I guess the customer would be none to happy to pay for the work?It's just a cheap spotlight, although when i looked at the lamp holder i could see no sign of damage. Which makes me think i'm going to have to re-wire the circuit.
Returning to your OP, what exactly was the fault that the customer was complaining of? Tripping RCD or MCB or some other problem?I've recently been called to a fault on a lighting circuit in a property, when asked if the occupier had done anything differently he told me that all he had done was change the lamps to the eco friendly ones.