How do I check the boiler output temperature? Isn’t it 60 as shown in the picture? I thought 60 was ok?
The HW setting is on the upper adjustment knob and does appear to be set at 60, but would need to be at least 70C to achieve 60C in the cylinder. The lower one sets the boiler's output temperature for when CH is called for.
However, I suspect you don't actually have a split system - one where boiler's HW output temperature can be set differently to the CH output temperature. Try setting the lower knob up to maximum and report back..
You probably have what's called an 'heat only boiler', which means it only responds to a demand for heat, but doesn't know or care where the demand came from.