The inportant parameter is the maximum current that can flow from cable to cable where they are clamped together in the terminal. This must be greater than the rating of the MCB protecting the circuit. Strangely I have only ever seen it quoted on data sheets for industrial sockets.That can't be it because it's exactly the same on a radial and would only be 13A maximum - unlike a double socket.I would suspect that as it would be in the ring, the restriction is on the rating of the input terminals
Many thanks lads, always learning
Just seen a 32A double pole switch, wouldn't this be better?
This is what I have decided to do and have now connected and run the 2.5mm² T&E spur to a single socket under the worktop.Using an FCU means that there will be the safety of a 13amp fuse to blow instead.
Perhaps better not to fit one, then?I expect you would connect a 2.5mm t+e on the load side of the switch. If there was a fault in this cable, the contacts on the 20amp switch could overheat before the MCB trips.
True, but unnecessary and only protecting that which need not be there..Using an FCU means that there will be the safety of a 13amp fuse to blow instead.
That wouldn't matter to the cable.Also, someone down the line could replace the single socket below the counter with a double and connect 2 high current devices.
You mean replace it with the original socket.This would overload the switch. Having a FCU prevents this, and means someone would have to consciously change out the FCU to achieve what they wanted
Perhaps better not to fit one, then?I expect you would connect a 2.5mm t+e on the load side of the switch. If there was a fault in this cable, the contacts on the 20amp switch could overheat before the MCB trips.
True, but unnecessary and only protecting that which need not be there..Using an FCU means that there will be the safety of a 13amp fuse to blow instead.
That wouldn't matter to the cable.Also, someone down the line could replace the single socket below the counter with a double and connect 2 high current devices.
You could say that was the fault of installing an unnecessary FCU when all would be well had the spur been run from the existing socket.
You mean replace it with the original socket.This would overload the switch. Having a FCU prevents this, and means someone would have to consciously change out the FCU to achieve what they wanted
No I didn't as the socket is in the next base unit and not in the washing machine area as I didn't want any water leaking near itHopefully you used an un-switched socket under the worktop? Saves accidental switch-offs when pushing the appliance back in.
It's not problem as I can run a cable from using the 16 amps radialYou could run another socket from this one for your freezer, but I wouldn't recommend it, it may be enough to blow the 13a fuse.
Is the reason I've listed why?
I mean, would a 32A switch be compliant?
Regulation 433.1.5 only lists BS1363 devices as being acceptable to be supplied from a RFC, and AFAIK this standard only applies to 13A socket outlets, and FCUs.