Arithmatic: MCBs, for which the CCCs are given, have a fusing factor of 1.45, BS1362 fuses 1.9. Therefore the cable should be derated by 1.45 / 1.9 = 0.763; 3 / 0.763 = 3.93. ... Just as BS3036 fuses have a fusing factor of 2, leading to 1.45 / 2 = 0.725 derating factor.
OK, so you are talking about a 'fusing factor' which relates to operation in 1 hour or less.
As you say, this point is never mentioned, but its a bit different from the situation with BS 3036s.
Given that BS 3036 fuses are 'singled out' (in 433.1.202),
any protective device other than a BS 3036 will satisfy 433.1.1(ii) if I
n≤CCC. In the case of a BS 3036, where the requirement (per 433.1.202) is that I
n≤(0.725 x CCC), it follows that, if 433.1.202 is satisfied, that I
2≤(2 x 0.725 x CCC) - i.e. I
2≤(1.45 x CCC) - so 433.1.1(iii) is
automatically also satisfied.
However, in the case of a BS1362 fuse (or any other protective device which is not a BS 3036 and does not have a 'fusing factor' of 1.45), this is
not the case. Such a device will satisfy 433.1.1(ii) so long as I
n≤CCC, but (as you have said above) it will
not satisfy 433.1.1(iii) unless:
I
2≤(1.45 x CCC)
hence (I
n x F )≤(1.45 x CCC) [where F is 'fusing factor')
hence I
n ≤(1.45 x CCC /F)
But, again, I doubt that this is ever thought about in the case of BS1362 fuses. I doubt, however, that this is a cause for concern since, as recently discussed, the CCCs for flex we work with are 'surprisingly low'.
Ignorance: Some manufacturers do not demand fusing for their appliances.
We can assume they do know what they are doing. After all, the requirement for an isolation switch is nothing to do with the operation of an appliance nor an electrical requirement nevertheless it too is included.
All agreed. A lot of small items of equipment do come with instructions that a 'small' (3A or 5A) fuse should be used in the plug, but I suppose that might be justifiable in terms of the size of the cable provided.
Kind Regards, John