Hello
I have found the sockets ring (in an out-building) is half wired with 1.5mm T+E instead of the correct 2.5mm. The cables are behind dry lined plasterboard, in front of the blockwork.
I am trying to rectify the situation with a minimal collateral damage as possible.
I have managed to replace two (short) lengths of the 1.5mm with 2.5mm (by drawing through the new cable with the old one).
There are now two lengths of 1.5mm cable, they go from twin-socket(0) across the wall around a corner and feed a single twin-socket(1), then move on to another twin-socket(2) around another corner. This length is approx 4.5m each leg. I have not been able to draw a new cable through this path and even if I did, I don't think it would meet clipping regulations.
As it is only destined to have a light load (table side lamp, phone charger etc.) instead of replacing these two cables (which is proving problematic), I am considering converting this twin-socket(1) to a fused spur, I would add a 13A fused spur box where the 2.5mm ends at twin-socket(0) and disconnect the return cable.
I do have a viable route to fit a 2.5mm cable to complete the ring from twin-socket(0) to twin-socket(2), the ring will end up smaller (not going all the way around the building), but it will be a ring leaving the spur as an outlier in the building.
Alternatively, does anyone have any other suggestion on how I can resolve this with minimal damage to the plasterwork?
I have found the sockets ring (in an out-building) is half wired with 1.5mm T+E instead of the correct 2.5mm. The cables are behind dry lined plasterboard, in front of the blockwork.
I am trying to rectify the situation with a minimal collateral damage as possible.
I have managed to replace two (short) lengths of the 1.5mm with 2.5mm (by drawing through the new cable with the old one).
There are now two lengths of 1.5mm cable, they go from twin-socket(0) across the wall around a corner and feed a single twin-socket(1), then move on to another twin-socket(2) around another corner. This length is approx 4.5m each leg. I have not been able to draw a new cable through this path and even if I did, I don't think it would meet clipping regulations.
As it is only destined to have a light load (table side lamp, phone charger etc.) instead of replacing these two cables (which is proving problematic), I am considering converting this twin-socket(1) to a fused spur, I would add a 13A fused spur box where the 2.5mm ends at twin-socket(0) and disconnect the return cable.
I do have a viable route to fit a 2.5mm cable to complete the ring from twin-socket(0) to twin-socket(2), the ring will end up smaller (not going all the way around the building), but it will be a ring leaving the spur as an outlier in the building.
Alternatively, does anyone have any other suggestion on how I can resolve this with minimal damage to the plasterwork?