I ring main is used to allow any section to be isolated to work on it, found mainly with HV supplies, and the cable can take the whole load, the ring final invented near the end of second world war allows the use of a smaller cable so uses less copper, I can't remember the size think it was 7/0.029 which was larger than 2.5 mm² when we went metric we were allowed to used 2.5 mm² for most cables, but 1.5 mm² with mineral insulated cables.
With 2.5 mm² we were allowed to use up to 85 meters, but this changed when the permitted volt drop was changed from 4% to 5% for socket outlets, so now 106 meters. Although the way this is worked out is not in the regulations, so is open to some debate, it is assumed 20 amp centre of the ring and 12 amp even spread, we do have a directive that non-portable items over 2 kW should be on a dedicated circuit, but except for the immersion heater no one seems to worry about that.
For you, best option seems a 20 amp MCB,