I had a Vaillant ecoTech Plus Open Vent boiler fitted in my loft about 6 months together with replacement Honeywell Frost (set at 3C) and Pipe (set at 20C) stats.
These replaced a 30 year old boiler (Ideal Classic NF40) and identical frost and pipe stats, again in the loft to my bungalow.
My queries are :
1. What could be considered a "normal" time period between the boiler "kicking in" (when the air temperature falls to 3C) and it stopping (when the temperature in the return pipe reaches 20C) and vica versa ?
2. Does the frost stat temperature (3C) or the pipe stat temperature (20C) have priority ?
3. If the CH is "on" and has reached temperature on my Drayton room stat and has turned off, will the boiler still "kick in" if the temperature in the loft falls to 3C ?

I ask as the new boiler seems to come "on and off" more (in the current cold weather) than my previous one.
Many thanks.
 
Last edited:
Sponsored Links
All could have varying answers. Are pipes insulated and were they previously? The frost stat and pipe stat should be wired in series (afaik) and will override any other controls. How long would be dependant on how much time it takes to heat up to the required temperature.
 
The pipework in the loft is now well insulated, better than before.
The frost stat are wired in series, does one override the other ?
 
I recently rewired my frost and pipe stats in my cold garage, and tested them by switching off the boiler so the pipes in the garage got cold, then turned the frost stat dial and had the pipe stat set to 20-30degrees IIRC. There was a long lag, pipes got really toasty before the pipe stat switched off the boiler. I was getting worried but in the end, boiler shut off.
 
Sponsored Links
The frost stat are wired in series, does one override the other ?

Because they are wired in series, both thermostats have to be calling for heat at the same time to trigger the boiler. So, as yours is currently configured, it must be 3 degrees or lower where the frost stat is located, and also 20 degrees or lower at the point the pipe stat is sensing.

Once the temperature where either the frost stat is located gets above 3 degrees, or the pipe stat gets above 20 degrees the frost protection is switched off.
 
Can anyone provide any additional information in reklation to my 3 queries ?
Because they are wired in series, both thermostats have to be calling for heat at the same time to trigger the boiler. So, as yours is currently configured, it must be 3 degrees or lower where the frost stat is located, and also 20 degrees or lower at the point the pipe stat is sensing.

Once the temperature where either the frost stat is located gets above 3 degrees, or the pipe stat gets above 20 degrees the frost protection is switched off.
Many thanks for the detailed response. appreciated.
 
Please forgive my ignorance, but as the pipework around my boiler is well insulated why are a frost and pipe stat actually needed ?
Is it for any other reason than just "insurance" ?
 
If there's no source of heat in the loft then, even with the best insulated pipes, they'll eventually get down to the outside air temperature. Insulation can't create heat, it can only retain existing heat for a certain time period
 
If there's no source of heat in the loft then, even with the best insulated pipes, they'll eventually get down to the outside air temperature. Insulation can't create heat, it can only retain existing heat for a certain time period
Thanks for that, which makes perfect sense but how about the (well insulated) pipework connected to the CW and F&E tanks in a loft - why are we not generally concerned about these freezing ?
 
If the house is unoccupied and has no heat on, then there is a very real chance that the CW storage tank and F&E tank pipes in the loft will freeze.
This can be averted for the F&E by putting combined inhibitor and anti freeze into the central heating system.
For the CW and indeed HW system it's usually the advice to drain these down if you plan to leave the house unheated in the Winter.
 
The point I am (unsuccessfully !) trying to make is why (in normal operating situation) boilers (in lofts) with well insulated pipework are protected by frost stats whereas (insulated) tanks with well insulted pipework are not. ?
I am not taking in any way about the situatuon where a property is unheated and/or unoccupied.
 