So how are you going to get out of that one, then?
You appear to be saying that the rating of the protective device is being determined by 'what is on the end of the cable', not the cable itself which you suggested is the only thing that it is protecting?
Fair point, but I was stating why, possibly, 6A protection is afforded to lighting circuits but perhaps it need not be.
Yes, you were, and it seemed a credible explanation. However, in terms of the point I was making, I don't think the reason/explanation really matters. The one point which is clear is that one does not need protection as low as 6A for 1mm² cable, let alone 1.5mm² - so, whatever the reason for the 6A protection (even if only habit/tradition/convention), it cannot really be for protection of the lighting circuit cable - although, as below, it might conceivably be to protect pendant cables.
After all what would happen to your lamps if the circuit was on a higher rated fuse? 6A is far to high for each lamp: even a 100W lamp is less than half an amp. Why aren't there FCUs before each lamp with 0.5A fuses?
I realise you're playing Devil's Advocate, but (apart from 'common sense') I suppose one answer to that question is that attempts to 'protect' a lamp with a small fuse would be futile and unnecessary; a lamp effectively acts as its own fuse, and does not present a fire risk which would be reduced by the presence of a 0.5A (or smaller) fuse!
However, switches and pendants are part of the circuit. Are the wires in pendants (and other light fittings) less than 1mm²? I shall have a look later. I concede they are unlikely to be overloaded but you wouldn't join a higher current wire with a 5A terminal block.
I thought that standard pendants used 0.75mm², or smaller, and I'm sure that I've seen wiring thinner than that inside some light fittings. I suppose this could be the answer to the 6A protection.
It has been stated before that a cooker on a 32A circuit consists of components of vastly different ratings with no further protection. None of the internal wiring remotely approaches 4mm² - and there is a 20W lamp.
That is very true - but to repeat the 'personal principle' I mentioned before, if one sizes the protection to be just large enough to sustain the load under normal operating conditions, one maximises the chances of the protective device operating in response to an internal fault before a fire arises (even if the current in question represents no risk to the final circuit cable). One can but assume/hope that the internal wiring within appliances is sized according to the 'normal' current carried by the wires in question - but almost anything can theoretically happen under fault conditions (depending on 'what ends up being connected to what').
I think that most of this comes down to common sense. Certainly in terms of my philosophy, I would not design a situation in which the rating of the protective device was the highest permissible in relation to the current-carrying capacity (CCC) of the cable if the situation was such that the actual current was never going to be anything like as great as that. With socket circuits one is generally forced to assume that the cables may be used right up to their CCC, but with dedicated circuits, it's often possible to use more sensibly tailored protection, far 'tighter' than would be needed to protect the cable alone.
Kind Regards, John.