But we're not talking about putting 32A down a 6mm cable, are we.
The 32A is the device protecting the cable - the design current is roughly 22A - the sum of the two MCBs in the garage CU - and that is the most that the circuit will be able to draw, so the volt drop will be lower.(and that's if the lighting circuit pulled it's full 6A, which is also unlikely.
This whole discussion came about because someone moaned about the 16A MCB that is currently installed not allowing discrimination with the 16A MCB in the garage - so I offer a solution and get picked to bits.
There was nothing wrong with my suggestion, unless you start thinking of extreme circumstances, and there's even less wrong with it now the OP has given us more detail
The 32A is the device protecting the cable - the design current is roughly 22A - the sum of the two MCBs in the garage CU - and that is the most that the circuit will be able to draw, so the volt drop will be lower.(and that's if the lighting circuit pulled it's full 6A, which is also unlikely.
This whole discussion came about because someone moaned about the 16A MCB that is currently installed not allowing discrimination with the 16A MCB in the garage - so I offer a solution and get picked to bits.
There was nothing wrong with my suggestion, unless you start thinking of extreme circumstances, and there's even less wrong with it now the OP has given us more detail