32 x 0.0073 x 29.5 = ..................?If he's worked it out, he's worked it out wrong!
6.89 V = 2.99%
That's all very well - for someone elses circuit
Ours is:
Design current - 22A
Volt Drop (3-core SWA) - 0.0064
Allowable volt drop - 5% = 11.5V
So,
22 x 0.0064 x ........ = 11.5
Answer: 81.67 meters
You still need to use the 2 core value unless you are talking about 3 phase, even if the cable is 3 core. The resistance of each conductor will be relatively the same in a 2 core or 3 core cable when used in single phase applications.
Allowable volt drop for a bog standard lighting circuit is now 3%, given we don't know the actual design current though.
I have had to drop 6mm submains down to 25A before owing to volt drop.