I would say that
@JohnW2 has answered most of the questions, before the RCD back I think around the 14th edition we went mad on bonding, but two things, one as John has said, if the sink is not bonded the shock will be less current, so often it is better not to bond, the second very revenant with a gas pipe, is you don't want a high fault current to pass down the gas pipe, as if enough to melt the gas pipe, it would cause a fire.
So some where on the gas supply we need an insulating part, so the earth bonding is not connected to a metal pipe which can conduct enough current to melt, so bonding as the pipe enters the house, is likely not going to connect the metal incoming gas pipe to the PEN, with a TN-C-S earthing system.
Two supplies should not have their earths interconnected, this can be a problem with metal frame buildings where there are multi-supplies to the same building, really TN-C-S in my option should be banned, but it should not be used with a metal framed building.
We have a problem, an air line has been fitted between two buildings, it is made of steel, and it connects the earth systems of two independent step down transformers, so the current could be quite high, but a 3" steel pipe will take a lot of current, and likely the railway lines also connect the earths together, so it is unlikely there will be a problem, and anyway air does not tend to burn.
When all the water and gas pipes were metal, any fault current due to loss of PEN would be shared between the service pipes, so no pipe carried excessive current, it is as pipes are changed to plastic when the problems arises, as any pipe which is still steel or copper, will end up carrying the fault current on its own.
Water pipes tend to be water cooled, it is only the gas pipe which can be a problem. I don't have gas, so no worries, but only the gas men/women know if the incoming pipe is plastic or not, and if the pipe has an insulating block or not.
It's not that they don't accept it, they are not the "experts" on electrics. They are required, by law, to notify you that it should be checked by a competent person if it might be necessary.
The question is who is the competent person, the gas man or the electrician? The kit to test if an electrode is earthed and a metal gas pipe is an electrode is this
I have used them many times, but it is not the sort of kit normally carried by electricians, if we can measure the resistance of the gas pipe, we can calculate how much current under fault conditions it will carry, so at say 46Ω at 230 volt it will carry a maximum of 5 amp. But I have no idea how much a gas pipe can carry, and the gas pipe could easy be 4.6Ω now looking at 50 amp, there is no fuse on the PEN conductor, the RCD does not disconnect it, so the electrician simply does not have the information to know if there is a insulator in the gas supply. So all he can do is connect to an earth terminal provided by the gas man. Failing that earth bond inside the house and cross ones fingers there is an insulator.