B
Bamber gaspipe
3m of 22 will deliver 8.7 m3/hr, well above an U6 meter capacity, as is 8m of 28mm 9m3/hr
Err. Thanks for that. Is there a point?
3m of 22 will deliver 8.7 m3/hr, well above an U6 meter capacity, as is 8m of 28mm 9m3/hr
3m of 22 will deliver 8.7 m3/hr, well above an U6 meter capacity, as is 8m of 28mm 9m3/hr
Err. Thanks for that. Is there a point?
3m of 22 will deliver 8.7 m3/hr, well above an U6 meter capacity, as is 8m of 28mm 9m3/hr
Err. Thanks for that. Is there a point?
There is if you read the OPs question and some of the rubbish that follewed.
How come your out on bail again.
3m of 22 will deliver 8.7 m3/hr, well above an U6 meter capacity, as is 8m of 28mm 9m3/hr
Err. Thanks for that. Is there a point?
Perhaps it was the tone of your previous post.
Completely pointless
Perhaps it was the tone of your previous post.
Completely pointless
About as pointless as you waffling on about how much gas 3m of pipe will deliver, as I said apart from stating facts known to every fitter on the planet what was your point
Put it another way that you may understand.
It's none of your dam business what I post, it was intended for the OP.
My god, why can't people just answer a simple question instead of constantly giving stupid comments?
Who said anything about doing it myself?
My comments were appropriate to a stupid question!!
Does your installer not know the answer??
Transco would only have 3/4" inlets yet the installer would have 28mm from the outlet. I recommend replacing the flex inlet with a 1" if possible. Available from http://www.bes.co.uk
The above statement proves your total lack of knowledge of the situation !!
You should not be giving advice on subjects that you have no understanding of!!
Stick to posting your googled knowledge of thermal stores!!
Hello All,
I need to upgrade my gas supply pipe from 22mm to 28mm for approx 8 mtrs from the meter before reducing back to 22mm. If the first few inches of supply pipe from the meter are in 22mm would this cause a bottle neck restriction i.e. 22mm-->28mm-->22mm?
TIA J
No, it will make no difference the first few inches being 22mm.
The point of using 28mm on many boilers is to reduce pressure drop between the meter and the appliance..
I wasn't aware that 28mm pipes exploded too
Hello All,
I need to upgrade my gas supply pipe from 22mm to 28mm for approx 8 mtrs from the meter before reducing back to 22mm. If the first few inches of supply pipe from the meter are in 22mm would this cause a bottle neck restriction i.e. 22mm-->28mm-->22mm?
TIA J
No, it will make no difference the first few inches being 22mm.
I have found it does. On some installations where the pressure drop was a little too much, replacing the outlet with a 1" x 28mm bent connector and around 1 foot of 28mm solved it.
If he needs 28mm back to the meter say for half the run, then a restriction in the run with impact.