Wow, go away for a couple of days and all sorts of weird stuff gets written.
Anyway, a bit of actual data now. I got an RGI (mate of a mate) to do a quick flying visit yesterday afternoon.
Gas pressure measured at boiler inlet:
Boiler running in low flame mode: 12mb
Boiler running in High Flame mode: 8mb
Boiler off, gas oven and all hobs running at full: 20.5mb
Cooker and boiler share a common 22mm connection to the gas meter that Ts off at the cooker and then travels a further 10m (in 22mm) to the boiler.
The total power of the oven and all four hobs running at full is approx 15kW.
So, a massive pressure drop when the boiler is running that certainly explains why I'm not seeing full power. Must be one hell of a restriction to be causing nearly 10mb of pressure drop when the boiler is only running at approx 10kW.
The results also suggest that the blockage occurs after the gas main Ts off at the cooker (since running the cooker at full blast does not cause much of a pressure drop). I've traced it through though and (externally) it looks fine with no kinks or bad joints.
The RGI reckons a new gas main from the cooker to the boiler might fix the issue but was unable to see where the restriction could be occurring.
Also, as regards the location, we live in the Pentland hills south of Edinburgh. Last snow was three weeks ago and temp at night was still -3 degrees two weeks back! Amazingly though, it hit 29 degrees in the shade on Saturday so looks like summer is finally here.
I agree that my heat loss calculations won't be super accurate but with solid walls, single glazing and no loft insulation in half the house, I reckon they won't be far out.