Recently had a new boiler installed (10 days ago) Ideal logic 2 30kw.
A pre-installation survery was done apparently.
Guy mentioned once it was installed and he was doing final tests that there was an issue with the pressure, between the meter and the boiler.
pressure with nothing on - 23mbar
pressure with the tap running - 20mbar
pressure at the boiler - 14.5mbar
and done a gas test, which was sitting 18.87kw, should have been closer to 27kw.
He reckons there is possibly to many 90 degree bends in the pipe and that the pipe may need replacing, question is, who should be responsible for this?
I didn't sign the work off as being complete and they are sending somebody out to look at it.
A pre-installation survery was done apparently.
Guy mentioned once it was installed and he was doing final tests that there was an issue with the pressure, between the meter and the boiler.
pressure with nothing on - 23mbar
pressure with the tap running - 20mbar
pressure at the boiler - 14.5mbar
and done a gas test, which was sitting 18.87kw, should have been closer to 27kw.
He reckons there is possibly to many 90 degree bends in the pipe and that the pipe may need replacing, question is, who should be responsible for this?
I didn't sign the work off as being complete and they are sending somebody out to look at it.