Ok cheers. There goes another £200. Sniff sniff.
Good call mate. So shutting the gas cock would not confirm that fault.Unless it is the control board giving the gas valve a short open signal immediately after the post-purge phase. Since fan is at rest any gas blown off will accumulate within the casing.
Turn off appliance isolation valve which is located on underside of boiler..I don't agree with that Nortonj. If you've turned off the gas stop cock and still smell the gas it could be gas in the boiler casing slowly leaking into the room.
This boiler utilises a zero governor (premix)......combustion fan RPM controls gas input to burner , with fan @ rest the servo diaphragm will remain closed and hence weep line pressure will be zero (no gas).Unless it is the control board giving the gas valve a short open signal immediately after the post-purge phase. Since fan is at rest any gas blown off will accumulate within the casing.
Turn off appliance isolation valve which is located on underside of boiler..
This boiler utilises a zero governor (premix)......combustion fan RPM controls gas input to burner , with fan @ rest the servo diaphragm will remain closed and hence weep line pressure will be zero (no gas).