Bad idea to me.
Quick additional question if I may... been offered another generator 2Kw, but it's only 110v.
If I wanted to use this, and hooked up a transformer with the 125-150m cable run, is there any advantage/disadvantage to doing this based on the 2Kw 230v generator we're currently using?
the extra genarator is effectively a 1kw generator at 230v....Thanks for the advice/thoughts so far.
The pump is borehole with borehole pump, but the origin is unknown, but it's single phase 230v.
Current wiring looks like a caravan hook-up cable (if this gives an idea?)
I'll try to get a plug-in energy meter at least it will give an idea of the load when operating.
Will have a digger dig 90% of the trench to lob the cable in, so should got smoothly.
*
Quick additional question if I may... been offered another generator 2Kw, but it's only 110v.
If I wanted to use this, and hooked up a transformer with the 125-150m cable run, is there any advantage/disadvantage to doing this based on the 2Kw 230v generator we're currently using?
Thanks again.
the extra genarator is effectively a 1kw generator at 230v....
How so?the extra genarator is effectively a 1kw generator at 230v....
Again looking at different on-line calculators for 118m: one says 4mm² another says 6mm², it also depends on choice of cable.My calculations allowing for corrected mV/A/m 4 mm² would just be within the permitted volt drop of 11.5 volt at 10 amp which is the max output of the generator for 118 meters, but I have not seen motor rating, and with an inverter drive likely you could get away with a larger volt drop.
Please explain your theorythe extra genarator is effectively a 1kw generator at 230v....
Was only to do a test regarding running current genny with distance of cable (as there seems a little ambiguity on sizing) I'm still intending to run with SWA.A caravan hook up cable should be at least 2.5 mm² and 25 meters long (±2 m) but in the real world often they don't comply. But you would need 5 or 6 cables, at £49 each from Halfords, many seem to be 1.5 mm² which does not comply with BS 7671.
You are looking at around £500 for the cable, you could buy another generator for less.
With respect,Was only to do a test regarding running current genny with distance of cable (as there seems a little ambiguity on sizing) I'm still intending to run with SWA.
Know a few people from whom I could borrow the hook up cables for a day or so.
You are correct regarding cable size, I have a couple that are like wrestling pythons and seen some that seem thinner than straws.
So this is clearly in true earth, so the question is where would you fit the earth rod? At generator or at bore hole, likely the SWA is a good enough earth wire, the problem is if the outer is ever damaged then steel can rust, so I would normally use 3 core, however with a generator nothing to stop you fitting an earth rod either end, so even if the SWA does rust, it would not matter, it would still be protected.The borehole pump