Getting BC to decide between 2 engineers?
Lateral restraint of a beam
In the Borough Council's view, this restraint could be provided by locating and fixing the beam tightly underneath the floor joists"
From the Handbook of Structural Steelwork
Full (continuous) lateral restraint is provided by:
(i) in-situ and precast flooring or composite decking, provided that the
flooring is supported directly on the top flange or is cast around it.
(ii) timber flooring, if the joists are fixed by cleats, bolts or other method
providing a positive connection.
(iii) steel plate flooring, if it is bolted or welded at closely spaced intervals.
If the beam isn't fixed in place (bolted or similar) then it can't be considered to be fully restrained.
Not sure there are many engineers who would treat that as fully restrained without the above, especially one without PI!
I'd usually take at least 1.0L for the effective length in such a situation, although where I used to work the partners were more conservative than that.
https://www.steelconstruction.org/r...nline-shop/productdisplay.html?product_id=453
Nervous, Page 162 gives the dimensions you are after...
The loads look about right. The only difference is I allready included self weight of beam so that was in twice. But removing it doesn't make a significant difference.
Regardless of the restraint, in my opinion the beam is perfectly adequate. BS5950 is really way over the top on safety factors and realistically you will never get anywhere near the total loads the beam is actually designed to take. In fact Eurocode 5 is available now and standard calcs on that are bringing in beams typically at least a serial size down on 5950. I'd like to bet a re-calc would show a 23kg beam in your situation. Unfortunately I don't have the EC5 software at present so I can't check it. (but I will do in the next week or so)
Here's a link to the Corus blue book (which is green for some strange reason) Go down to columns and read across for the flange sizes.
http://www.tatasteelconstruction.co...s/advance_section_properties_for_students.pdf
Really, my advice would be get the approval from building regs. I wouldn't consider knocking anything about myself.
It's very unlikely that the Building Inspector will be able to tell the difference between a 23 and 30.
Not if he's got a ruler!
But would he know what to look for? The Council's engineer would if got to the point where they were actually concerned that the 'right' beam was installed.
My own experience is that the Council's engineer doesn't actually go round to check what's been installed, but simply checks and OKs the figures given to him. Meanwhile on site, I've seen Inspectors measuring the overall depth and flange-width of beams, but few seem to appreciate that, apart from the smaller UBs, most come in different weights.
(At least that's how it seems to work up here)
Would this not be eurocode 3- BS EN 1993 ;)
Where I live any of the BCO's I've dealt with are familiar with the different weights of beams available.