A small empty box is almost the same price as a large empty box. Unless there isn't enough space to physically fit a larger enclosure, it would be insane not to.is one wise to purchase a CU with plenty of spare ways
None of the editions specify any particular arrangement of devices, things like '18th edition consumer unit' are terms invented by the marketing departments of various manufacturers.Split load and dual RCD consumer units should not be considered for any new installation.
Has this been ruled out in the 18 Edition ? I have not read anything to this affect.
However:
- 314 Division Of Installation requires that 'every installation shall be divided into circuits as necessary ... ' for various reasons, and shoving half of the installation onto a single RCD is in no way complying with that. No one ever wanted the upstairs lighting to fail because someone shoved a knife into the toaster, or their home office to be disconnected because rain got into an outside light.
- Much modern equipment has a certain amount of residual / leakage / protective conductor current in normal operation, and the maximum permitted is 30% of the RCD rating, which is only 9mA for a 30mA RCD. As a single filter in an appliance could result in 1-2mA, it's very easy to be way over the 9mA when multiple circuits are combined onto a single device. This will result in the RCD tripping in normal operation.
- Adding another circuit to a dual RCD consumer unit is likely to compound that problem further.
- The inverter for a solar panel installation cannot be connected to a circuit which is supplied from an RCD which covers multiple circuits, as disconnection times will not be met.
- Certain types of equipment require certain types of RCD - with a dual RCD consumer unit, there is no option to install non-RCD circuits or other types of RCD as required. Not possible to install certain types of RCD downstream of others either.
- When AFDDs are mandatory for some/all circuits, installation of those is just a matter of replacing an RCBO with an AFDD. With a dual RCD consumer unit, the only option is a new consumer unit.
Whether they have a functional earth connection depends on the internal design of the electronics - some do, some do not. Most of the modern ones do not.
Single pole RCBOs are suitable for use on TN systems. For TT, single pole with switched neutral is required - or double pole which are generally twice as wide.
Some manufacturers make both types, others only one, as there is nothing wrong with using those with a switched neutral on a TN system even though that isn't required.
The problem isn't one of tripping, but the exact opposite. Type AC RCDs only work properly for AC resistive loads such as an immersion heater or incandescent lighting. With other loads connected (which includes 99% of electronic equipment, LED lighting, inverter drive motors and much more), Type AC may not work properly or at all.and note that this could cause issues for the AC type RCD, an A type is recommended - but so far though there has been no tripping.
Surge protection is required for the vast majority of installations. It is not optional, or something the homeowner can choose not to have.