Is that a challenge?What this posting does demonstrate is that the instructions for controllers leave a lot of questions unanswered if D Hailsham cannot find the answer!
1. If there was no link between L and R on the boiler, it would not run at all.
2. If there was no link between 0 and 24V on the boiler, I suspect that the receiver would not work.
3. The Climapro must be set to Mode 0 if the HW is indirect (via a cylinder)
4. No-one has considered the possibility that the Climapro controller or the Smart wiring centre may be faulty.