John, you have a valid point. I don't 'need' to balance the house across three phases but I AM looking to have maybe two rings per floor.....
That may or may not be 'sensible'/necessary but it's the actual loading which matters, regardless of the number of circuits (you could have one circuit for each socket, if you wanted, but that, in itself, would not mean any more load). Is there a specific reason why you want two rings per floor? - 'upstairs' rings are usually only lightly loaded.
Also, seems like I may as well eradicate the existing 'unknown qty' CU in the process... Yes, the tin box is around 100quid and the SP rcbos seem to be about 25quid...as opposed to mobs at a fiver... Now could I just run the SP rcbos for the house, about 13 or 14 circuits ...
Sure, that's essentially what I was saying, BUT ... if you are going to replace the CU, you could replace it with a dual RCD one and then use (much cheaper) MCBs, rather than RCBOs. The only downside (compared with RCBOs) is that a fault on a circuit would then trip the RCD serving several circuits - but that is the arrangement that the majority of houses have.
...and install a TP rcd for the TP cable, run it to the garage with either a small TP distribution board and mcbs or for the one off, a small surface mount TPN socket for the lathe (just need to get a suitably rated mcb in there...
Essentially, yes. The only addition to that is that you would need overcurrent protection (probably a TPN switch-fuse) as well as the RCD to protect the cable to the garage - otherwise the only thing protecting it would be the supplier's service fuses. Assuming you were running armoured cable to the garage, the RCD could be at either house or garage end ...or you could use a (probably very expensive) 3-pole RCBO at the garage end.
Or have I now lost the plot....
Not at all - see above.
Kind Regards, John[/quote
Only reason for splitting the circuits per floor is easier install and maintenance with the added advantage of only part of the floor is out should a circuit trip. Its not a load or an area issue (although one floor area would be close to the 100sq meters rule)
If i were to distribute the circuits over the 3 phases i presume its better to keep the distribution floor by floor rather than front of house back of house due to the potential of having the two phases potentially close together providing an increased risk of accidental contact with 415volts
Ah, yes...missed the overload protection for the cable...rcd surely though better at the house end of the cable as it then protects from damage to the the cable and the distribution in the garage, rather than just the distribution in the garage...