When you have CH only, the pump runs, but do you get 240v to the boiler?
Are you saying that in CH+HW mode the water circulates through the rads OK and they heat up properly?It appears in CH only mode the boiler is cutting out on the overheat stat due to lack of water flow.
Not surprised they got red hot. There was nowhere for the water to circulate (unless the flow and return are connected together at the end or there is a bypass valve)I then tried closing all the radiator valves, feed and return and then ran up the system with the valve head removed and manually moved the valve to the CH only position. The feed pipe to the pump and on the CH side of the valve became red hot.
That's to be expectedI then opened a radiator on the landing only a small amount and it got red hot.
How hot is "red hot"?I slow went round and opened the other rads a bit and they eventually all got red hot
Can you post a pic (use Upload Pics) of the airing cupboard showing the general layout of the cylinder, pipework etc.There seems to be a lot of air in the system but not sure how to cure this as no bleed in the loft or by the cylinder.