Don't quite understand your statement 'It appears in CH only mode the boiler is cutting out on the overheat stat due to lack of water flow'
How can this be if you can't get CH only mode?
If you can get CH only and the boiler cuts out shortly after lighting then it's not a actuator head problem. It's more likely due to lack of water flow indicating a pump problem.
I have experienced this type of problem and removed pump for examination. The inlet and outlet orifaces were reduced from about 25mm down to about 8mm with a build up of silt. As pump was 11 years old, opted for new pump and problem cured.
How can this be if you can't get CH only mode?
If you can get CH only and the boiler cuts out shortly after lighting then it's not a actuator head problem. It's more likely due to lack of water flow indicating a pump problem.
I have experienced this type of problem and removed pump for examination. The inlet and outlet orifaces were reduced from about 25mm down to about 8mm with a build up of silt. As pump was 11 years old, opted for new pump and problem cured.