I have never seen that function on any RCBO, and certainly not Hager ones. Only come across it on a (very) few RCDs like MK.Some RCBOs that have tripped need to have the operating lever pressed further down before being lifted up to switch the RCBO back ON.
More likely. Probably a European regulation Hee heeMaybe the indicator is to show the true state of the RCBO
I presume you mean 6kA and 10kA - not kVA.I think Hagar used to be 6kva domestic and 10kva commercial, and they have now phased out the 6Kva ones
That would be very useful (at times) if it were the case but, as you say, it is probably wishful thinking!I would like to say it flags a colour in the window if the Rcd element has caused the trip. Rather than over current. But that’s probably wishful thinking !
As a matter of interest, when/why are the 10 kA ones used? In terms of domestic installations, the general belief seems to be that when the dispensation for 6 kA devices does not apply (e.g. if the devices are not part of a 'type-tested CU') then one has to use 16 kA ones.As far as I am aware, Hager do a domestic and a commercial RCBO, the main difference being the length of the tails. The domestic RCBOs were only available in 6kA and didn’t have the window, and the commercial ones were 6kA or 10kA and had the window.
I thought that one had to consider not just the actual (i.e. as measured) PFC (which will virtually never be >6 kA in a domestic installation) but, rather, the maximum 'theoretically possible' PFC, which, 'on enquiry' the DNO will always say is 16 kA - and that, per 536.4.201, use of 6 kA devices would then only be acceptable if they were part of a 'type-tested' CU to BS EN 61439-3, "including the 16 kA conditional short circuit test" which is apparently in Annex ZB of that Standard (and which, I believe, takes into account upstream protection by a cutout fuse ≤100A). Is that not the case?I can’t remember where I was taught this, but AIUI, with a standard domestic supply, in the unlikely event that the Ipfc exceeds 6kA, it is still permissible to use 6kA devices as the cutout (assuming it is not BS 3036) will provide sufficient protection to the installation.
As far as I am aware, Hager do a domestic and a commercial RCBO, the main difference being the length of the tails. The domestic RCBOs were only available in 6kA and didn’t have the window, and the commercial ones were 6kA or 10kA and had the window.