The fundamental with a heat pump is the flow rate.
If too many zones are closed, or the system is restrictive the flow rate will drop.
Slightly too low will lower the COP (efficiency), if its too low the heat pump wont run at all.
This can be mitigated with a header or buffer, with some loss of efficiency. (Some heat lost due to mixing, and additional pumps required)
The traditional method is to have a boiler that makes too much heat, and throttle it back with thermostats.
Heat pumps use modulation and weather compensation to match the heat output to the building losses.
On/ Off controls do not work well with heat pumps.
If too many zones are closed, or the system is restrictive the flow rate will drop.
Slightly too low will lower the COP (efficiency), if its too low the heat pump wont run at all.
This can be mitigated with a header or buffer, with some loss of efficiency. (Some heat lost due to mixing, and additional pumps required)
The traditional method is to have a boiler that makes too much heat, and throttle it back with thermostats.
Heat pumps use modulation and weather compensation to match the heat output to the building losses.
On/ Off controls do not work well with heat pumps.