The house i am moving into has a sealed central heating system with a regular condensing boiler which is a British Gas 330 (Glow-Worm HXI?). The main heating ring main pipework is 28mm and the it has 16 radiators all teed into the ring main on 15mm pipework. All the radiators except for the hallway where the roomstat is have TRV's, and there is also an auto bypass valve between flow and return.
Currently, the upstairs radiators at the far end of the house (4 of them) never get fully hot like the rest of the radiators. The system is 5 years old and all the radiators were brand new and fitted at the same time as the boiler.
The pump is a Grundfos 15-60 standard pump and the boiler has been range rated to 24w with a temp differential of 12 degrees between flow and return, according to the BG commissioning paperwork
In the manual for the BG 330 boiler, it says that at the minimum output of 18kw the flow rate is 773.8 litres per hour with a 1.00 meter head, and at the top end of 31kw the flow rate is 1289 litres per hour with a 2.55 meter head to be able to maintain a max of 20 degrees differential between flow and return.
If i enter this data on the Grundfos pump size calculator, it comes up with a recommended pump as the Grundfos Alpha2 25-40. Would that sound right to you?
My thinking is that the 15mm nominal size of the pump inlet and outlets with the 15-60 pump is potentially causing too much of a restriction. would anybody agree with that?
Currently, the upstairs radiators at the far end of the house (4 of them) never get fully hot like the rest of the radiators. The system is 5 years old and all the radiators were brand new and fitted at the same time as the boiler.
The pump is a Grundfos 15-60 standard pump and the boiler has been range rated to 24w with a temp differential of 12 degrees between flow and return, according to the BG commissioning paperwork
In the manual for the BG 330 boiler, it says that at the minimum output of 18kw the flow rate is 773.8 litres per hour with a 1.00 meter head, and at the top end of 31kw the flow rate is 1289 litres per hour with a 2.55 meter head to be able to maintain a max of 20 degrees differential between flow and return.
If i enter this data on the Grundfos pump size calculator, it comes up with a recommended pump as the Grundfos Alpha2 25-40. Would that sound right to you?
My thinking is that the 15mm nominal size of the pump inlet and outlets with the 15-60 pump is potentially causing too much of a restriction. would anybody agree with that?