A variable duty pump should be set to give a temperature difference of no greater than 20°C between the flow and return, with the thermostat set at “MAX”, which is about 80°C, to give a flow rate as given in the table.
A variable duty pump should be set to give a temperature difference of no greater than 20°C between the flow and return, with the thermostat set at “MAX”, which is about 80°C, to give a flow rate as given in the table.
DH is an armchair expert and not an installer. But I am impressed by how well he does without the practical experience.
I prefer to use a lot of practical experience as theory and reality dont always match well. As in gas pipe sizing where the measured resistance can by up to twice the calculated value.
We can measure temperature and boiler input power very accurately but we cannot normally measure flow rate directly.
OK, glad to say this is all resolved now. Fitted a UPS 25-80 180 pump (230 volt version) and on its maximum output this has brought the maximum temperature delta down to 23c on the boiler.
(Took a week for the pump to get delivered, just fitted it this evening.)
This is marginally outside the range for the boiler, but importantly it doesn't reach a 30c delta and trigger an s.53 code.
Heating controller can now be programmed to turn off heating at night!
Thanks to everyone for all their input into this thread, it's been really helpful, and very much appreciated.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local