Diyitall wrote
By the same token you should be looking at 35mm from the boiler until the split.
35mm is grossly oversized.
Guessing again are we ?.
What for a 35kw load I don't think so balski
Diyitall wrote
By the same token you should be looking at 35mm from the boiler until the split.
35mm is grossly oversized.
Guessing again are we ?.
By the same token you should be looking at 35mm from the boiler until the split.
When you say the first rads branch off close to the boiler, you are aware you can only tee off the common return once.
The boiler itself has 28mm primaries so 35mm is not an option.
By the same token you should be looking at 35mm from the boiler until the split.
When you say the first rads branch off close to the boiler, you are aware you can only tee off the common return once.
The boiler itself has 28mm primaries so 35mm is not an option.
I wasn't aware you could only tee off the common return once - the central heating part of the system was already there when we moved in. What is the consequence of more than one tee?
The boiler itself has 28mm primaries so 35mm is not an option.
You can use any flow and return pipes you choose! I saw a boiler today with 22 mm connections which had 35 mm pipes to the manifolds.
Just why do you think you cannot use 35 mm ???
Tony
Unless you house a football team you are unlikely to have to use the full reheat capability very often.
For half the year you have to share boiler output with the CH. Without that you have full pump and boiler power for the HW.
I would use a 28 mm motor valve and a 22 mm pipe run with two 22 mm gate valves for isolation and balancing if it were ever required.
The cylinder heat absorption is only at the maximum when the stored water is at about 10°C. It rapidly reduces as the temperature differential falls so the 22 mm pipe run will have little effect for most of the time.
Tony
doitall";p="873059 said:DIYAddict";p="873039 said:If you tee off the common return more than once you get reverse circulation.
You will need to take the cylinder return back to the boiler so its the last tee before the boiler.
Ah. I wonder if that explains why some of the radiators suck in air even though the f&e tank is plumbed in correctly for positive pressure throughout. I must admit I'm not quite sure of the difference between teeing off the common return and a radiator's return pipe joining the common return where it's supposed to.
I've definitely been intending to make the cylinder return the last tee before the boiler.
Agile and Doitall, looks like I still have a lot to learn about plumbing! I'd assumed that 35mm would offer no benefit if the flow was constricted at the boiler by 28mm connections, in the same way that 30A cable would be no advantage if connected to the end of 5A cable.
?
Thanks Agile.
So, if the constricted bore is unimportant if not too constricted and/or not too long, why do shower pump manufacturers insist on full bore valves instead of isolator valves? Playing it safe I suppose...
Cheers, Paul
doitall";p="873938 said:By the same token, the gravity cold feed to the cylinder should be increased to match the output of the pump and any other drawoffs.
I'm using a 28mm cold feed and the tank is in the loft above. The ceilings are quite high (4m) so I'm hoping that will give enough flow. The shower pump will be sited on the floor at the base of the cylinder.
Again this was on the (mistaken) assumption that the size of the cylinder boss dictated the plumbing bore. Do you think 28mm will be enough? It's not too late to change to 35mm.
I'm siting the cylinder cold feed above the other cold feeds on the tank to prevent scalding should the tank run dry.