The good news is that I now have a copy of BS 7609 "Code of practice for Installation and inspection of uninsulated compression and mechanical connectors for power cables with copper or aluminium conductors". Catchy title eh!
The bad news is that it is limited to conductors having a cross-sectional area equal to or greater than 10 mm2 for copper and equal to or greater than 16 mm2 for aluminium, so it doesn't help us much with domestic installations. However it is clear that it applies to both stranded and solid conductors.
It refers to hexagonal or circumferential crimping, which seems self-explanatory, and indent crimping, which is what I was trying to describe earlier. It also points out that the connector, die-set and tooling should be as specified by the manufacturer, which is likely to be difficult to achieve in practise given that most people will buy the connectors and tooling separately.
There are some examples of unsatisfactory crimps, which include compression too far from the end of the connector, or too close to the end, as well as over-compression due to incorrect tooling.
Another bit of wishful thinking is the following statement "At suitable intervals not exceeding 12 months and, depending upon tool types, usage and manufacturer’s recommendations, the tools should be submitted to a suitably qualified maintenance, test and inspection authority". Anyone had their crimping tool recalibrated recently?
I'll keep on trying to find a more appropriate standard.