This is where my thoughts differ in the interpretation from you.
I read "two individual protective conductors, each complying with...." as meaning two individual protective conductors, each complying with...
i.e. "
this individual protective conductor, complying with... and this
other individual protective conductor complying with...".
There really is no more reasonable interpretation, and in fact I'd hardly call it an "interpretation" at all - English is my first language, and it's written in English. I just read it, and understand it, in the same way that if I read "two individual fillets of white fish, each weighing about 250g" or "you'll need two individual pieces of 4x2, each 8' long" I'd know exactly what it meant without engaging in tortuous "interpretation".
Maybe the fact that you feel you need to "interpret" what is written rather than just simply reading it is part of the problem here?
If the individual protective conductors are sized in accordance with section 543 and they form a ring then I don't see the problem.
The problem is that if in 543.7.1.3 you decide that "protective conductor" means one of the individual links, that doesn't allow you to just have a single one as per (i) and (ii), nor two of them as per (iii), nor does it allow you to have
each one complying with 543.2.
Do you take into account the disclaimers in those?
Yes, I do. I also take into account they are written by engineers from the IET and are aimed at the likes of myself to help comply with the regulations.
Maybe they too are written by people who cannot or will not read "two individual protective conductors, each complying with..." in the simplest, most obvious and most normal way.
And do you take into account that there are clearly a lot of people who cannot or will not read what the regulations actually say?
Yep, and those that try to understand what the regulations say and apply them in real life situations.
There is no "try to understand", or at least there wouldn't be if you didn't insist on artificially creating a need. "When we go camping we'll need two tents, each capable of sleeping 4 people" does not need any effort to understand it - you read it, it's plain what it means and you understand it.
"We're looking for for volunteers for transport duty - we'll need two drivers, each with a vehicle that can carry 3 passengers" does not need any effort to understand it - you read it, it's plain what it means and you understand it.
"Two individual protective conductors, each complying with the requirements of Section 543" does not need any effort to understand it - you read it, it's plain what it means and you understand it.
Or at least, you should.
Using the guidance notes and on site guide help cross this boundry - the regs state what needs to be done, the guidance notes and OSG aid in how to do it.
But you are using guidance documents, or if tasked would write guidance documents yourself, which do not show you how to do what the regulations state - they show you how to do something different.
And do you take into account that what the guidance documents say clearly contradicts what the regulations say?
I wouldn't say clearly contradicts.
However you define and count them, this diagram:
does not show two individual protective conductors.
And do you take into account that it is the Wiring Regulations which define BS 7671, not any guidance publications?
Like I said above, it is the regs which say what needs to be done. The guides offer assistance in how to accomplish it.
So in other words what is written in the Regulations is what defines compliance with BS7671, not what's written in the guides.
Hence the disclaimers in the latter.
Individual as in separate from each other? 2 protective conductors at each point each providing a separate and independant path back to the MET.
But that's not what the regulations say.
They don't say you must have "two protective conductors at each point each providing a separate and independent path back to the MET", they say that the circuit must have
a high integrity protective connection consisting of two individual protective conductors...
The current is flowing through 2 separate paths through separate protective conductors.
But if that is how you decide that there are two individual protective conductors you don't then have a situation where
each of them complies with the requirements of Section 543.
And 543.7.1.3 (iii) says that
each of them must.
I don't claim the diagram to show any sort of compliance with 543.7.1.3 (i) and (ii), these require a protective conductor to connect the item back to the MET in the sizes stated.
OK - assuming that the sizes are OK, do you claim that the layout of the protective conductor(s) complies with 543.7.1.3 (i) and (ii)?
So it is OK for the conductors to be classed as separate conductors if connected but looped at the MET, but not if they are connected and looped at an accessory? The idea of high integrity earthing is to either ensure the path to earth is not lost or to provide another path should one be broken.
Never mind what the reasons for high integrity earthing are - will you please stop evading a request for you to explain how you designate and count individual conductors.
If you had a continuous length of copper wire with little U shaped bends in various places, when does it become two conductors and how, and why when whatever the operation is that takes it from one to two is carried out another n times doesn't it take it to n+2 conductors?
Can you clarify what the numbers mean?
I can see individual lengths of protective conductor with:
. a 1 at each end
. a 2 at each end
. a 1 at one end and a 2 at the other
so they can't be saying "this is protective conductor #1 and this is protective conductor #2"
Also that drawing has 5 components each labelled "protective conductor" - can you explain how they relate to either the requirement in 543.7.1.3 (i) and (ii) for "
a single protective conductor" or the one in 543.7.1.3 (iii) for "
two individual protective conductors"?