Dear Experts,
My flat is wired predominantly with metal conduit, with the conduit itself as the earth. For one of the socket ring circuits I have the following numbers in an EICR:
r1 = 0.50
rn = 0.51
r2 = 0.68
(R1+R2) = 0.68
Zs = 1.31
Two questions:
Firstly, this I believe is "test method 1", but I don't think that is suitable for a steel conduit installation, is it? Or have I missed something.
Secondly, the measured Zs is high. How much do I need to worry about this, and how can I try to diagnose where the problem might be?
My flat is wired predominantly with metal conduit, with the conduit itself as the earth. For one of the socket ring circuits I have the following numbers in an EICR:
r1 = 0.50
rn = 0.51
r2 = 0.68
(R1+R2) = 0.68
Zs = 1.31
Two questions:
Firstly, this I believe is "test method 1", but I don't think that is suitable for a steel conduit installation, is it? Or have I missed something.
Secondly, the measured Zs is high. How much do I need to worry about this, and how can I try to diagnose where the problem might be?