And why is that (r1+r2)/4?Because the fault will not cover the entire ring length as it stands as a measured value end end. the true earth fault path is the R1+R2 value.
Current won't only flow along the shortest path.im thinking the shortest distance back to suppliers transformer back up through live to opperate o.c.device
Wired in 2.5mm twin and earth ( r1+r2 value 19.51 m.ohm/M )
Approx length of run 35 Metres
Type B circuit breaker max E.F.L. 1.16ohm (on site guide)
Zs = 0.8 + (0.68 ) = 1.48ohm
Is it always 4?
Well raise my rent!We got an Ohms sign now too Ω
No - it's always ¼.The R1+R2 value is only exactly 1/4 of the r1+r2 value if the conductors are of equal CSA. If they are not then it is approx. 1/4.