I had Hive installed about June and all seemed good.
Now in recent times (as we use the CH) I've noticed the CH stays on i.e. the boiler goes through the motions of heating the water turning off for a while presumably as it reaches it's own temperature and then coming back on again 5-10 minutes later regardless of what the thermostat is saying. Also looking at the light on the Hive box it's basically saying the heating is off and the pump acts as normal, runs for a while after the boiler then cuts out.
The HW (tank) appears to work normally.
Now from poking about the internet this looked to be a CH 3 port valve issue and the valve and electronic motor may need replacing because they're stuck or the motor is worn out.
Up until now I've been cutting the power in the airing cupboard where everything but the boiler is and during this process I can hear the CH 3 port valve rotate back, reset itself and the heating stops until the Hive thermostat kicks in as it gets below threshold etc but...
A few days ago I noticed if I place a call (boost or on) to the HW I can hear the CH 3 port valve rotate back and then if I turn the HW off or leave it to run the CH is ok and doesn't just run constantly.
For me this implies the CH 3 port valve is working as it rotates back and forth not stuck, could the wiring be incorrect or could it still point to a faulty CH 3 port valve?
Now in recent times (as we use the CH) I've noticed the CH stays on i.e. the boiler goes through the motions of heating the water turning off for a while presumably as it reaches it's own temperature and then coming back on again 5-10 minutes later regardless of what the thermostat is saying. Also looking at the light on the Hive box it's basically saying the heating is off and the pump acts as normal, runs for a while after the boiler then cuts out.
The HW (tank) appears to work normally.
Now from poking about the internet this looked to be a CH 3 port valve issue and the valve and electronic motor may need replacing because they're stuck or the motor is worn out.
Up until now I've been cutting the power in the airing cupboard where everything but the boiler is and during this process I can hear the CH 3 port valve rotate back, reset itself and the heating stops until the Hive thermostat kicks in as it gets below threshold etc but...
A few days ago I noticed if I place a call (boost or on) to the HW I can hear the CH 3 port valve rotate back and then if I turn the HW off or leave it to run the CH is ok and doesn't just run constantly.
For me this implies the CH 3 port valve is working as it rotates back and forth not stuck, could the wiring be incorrect or could it still point to a faulty CH 3 port valve?